Discuss Wylex RCBO Test - To middle versus bottom position in the Electrical Tools and Products area at ElectriciansForums.net

Reaction score
1
Last week I took the opportunity of having the mains power off to test the RCBOs in a Wylex Consumer Unit, fitted nearly 5 years ago, which has the following:

1 off NHXS1B40, 4 off NHXS1B32, 2 off NHXS1B16, 3 off NHXS1B06 and 1 off NHXS1B25

Now on Test, the B40 switch went to the mid position, but all 10 of the other RCBOs went to the bottom off position.

Does this mean that the B40 is faulty in some way?

Or is it a feature so that you know it has tripped and have to turn it off and on, rather than just on? - Which I have seen with some other RCBOs.

If so why did the other 10 off RCBOs not do the same.

Do any of you have any experience or knowledge about this?

I tried emailing Wylex but they just said: "Sounds like there might be a latching problem or the contacts inside the RCBO" and that the circuit and RCBO be inspected!

They did not answer whether this is a feature or a fault specifically!

Thanks in advance.
 

Reply to Wylex RCBO Test - To middle versus bottom position in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

I had Scottish Power moving a supply this morning from one building to another so an extension could be built. I had everything ready for them...
Replies
1
Views
790
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
732
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
2K
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Hi all, Turned off RCBO (Lewden B32 6kA) to fit new socket. I always test for voltage with both a volt stick and voltage tester. Volt stick went...
Replies
2
Views
880

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock