Hi all,
Turned off RCBO (Lewden B32 6kA) to fit new socket. I always test for voltage with both a volt stick and voltage tester. Volt stick went mad. Went back to check the RCBO and its switch was in down position but for some reason not actually "off". Seemed a bit wiggly - switch wasn't pressed hard against the bottom like it's supposed to be. Flicked on and off a few times and was fine.
I will get somebody to replace it. My question is how urgent is this? This type can trip fine (using test button) in when held in place with finger, so I'm not worried about the movement of the switch itself, but I am concerned that there is something not right with the internals which might cause it to not trip properly.
Also, I have 3 other B32s in the consumer unit. Is it worth getting them replaced considering they are probably from the same batch?
Thank you.
Turned off RCBO (Lewden B32 6kA) to fit new socket. I always test for voltage with both a volt stick and voltage tester. Volt stick went mad. Went back to check the RCBO and its switch was in down position but for some reason not actually "off". Seemed a bit wiggly - switch wasn't pressed hard against the bottom like it's supposed to be. Flicked on and off a few times and was fine.
I will get somebody to replace it. My question is how urgent is this? This type can trip fine (using test button) in when held in place with finger, so I'm not worried about the movement of the switch itself, but I am concerned that there is something not right with the internals which might cause it to not trip properly.
Also, I have 3 other B32s in the consumer unit. Is it worth getting them replaced considering they are probably from the same batch?
Thank you.