Discuss Type A rcd for cooker or type AC OK? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,607
My builder has sprung a job on me.
New circuit required for a hob.
The CU has a single 30mA RCD, type AC.
I am still unsure exactly when I should insist on type A, and when I should just advise.

Would you guys be insisting on type A in this case, thus fitting a new CU (as it is an old NSB wylex board with an RCD taking up 3 slots (WSES 100/2). Pretty sure there wouldn't be a type A available)).

The MI would be interesting to read, but I don't have them.

Not sure how be are supposed to determine if there is a possibility of pulsating, residual DC.

Thanks.
 
You need to bear in mind what else is on that RCCB, and which could prevent it from operating correctly. It's not just the load you're adding which is relevant - DC from other parts of the installation could render the RCD protection ineffective for your addition/alteration.
 
We should always 'advise', as our recommendations to clients should always be based against current best practice. However, whether we need to 'insist' is an entirely different animal. For example - in the unlikely event that the cable feeding the circuit is surface clipped then there's no need for any RCD in the absence of a MI that stipulates one (assuming no socket outlet on the oven switch....). As already said above, whilst my personal gut tells me you'll be fine to stay on an AC, only you know what you're installing and what's there already. Also, one assumes that there was an existing oven/hob as part of the original install anyway?
 
We should always 'advise', as our recommendations to clients should always be based against current best practice. However, whether we need to 'insist' is an entirely different animal. For example - in the unlikely event that the cable feeding the circuit is surface clipped then there's no need for any RCD in the absence of a MI that stipulates one (assuming no socket outlet on the oven switch....). As already said above, whilst my personal gut tells me you'll be fine to stay on an AC, only you know what you're installing and what's there already. Also, one assumes that there was an existing oven/hob as part of the original install anyway?
You would think there is already one there, but the builder hasn't mentioned this. He's pretty savvy, and I believe he would have mentioned this during our chat if there was one.
 

Reply to Type A rcd for cooker or type AC OK? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
756
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
242
i have faild napit annual assessment with silly mistake of using on consumer unit type AC rcd instead of Type A rcd. i bought type A rcd but they...
Replies
6
Views
766
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
650

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock