Discuss Type of DNO supply question in the UK Electrical Forum area at ElectriciansForums.net

B

brenfox

I was installing a new control panel in a pumping station kiosk the other day. Sometimes I am required to `enter` the DNO supply to insert the earth cable on what is normally a TNCS system. To my surprise the supply was a single core with the armourings supplying the system earth but no neutral. Not sure what to think of this? Pretty sure this works fine in electrical theory but...
 
......
 

Attachments

  • Concentric_neutral_cables.jpg
    20 KB · Views: 151
I was installing a new control panel in a pumping station kiosk the other day. Sometimes I am required to `enter` the DNO supply to insert the earth cable on what is normally a TNCS system. To my surprise the supply was a single core with the armourings supplying the system earth but no neutral. Not sure what to think of this? Pretty sure this works fine in electrical theory but...

It will be concentric cable, associated with TNCS/ PME earthing.
 
The other type you may come across is split concentric, where you have the single core and two layers of conductor one normally unsleeved and the other sleeved over each conductor.
 
I would of thought you should firstly inform the DNO that you wish to use their earthing arrangement.
Also, you shouldn't be connecting directly to the DNO equipment.
 

Reply to Type of DNO supply question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
641
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock