Discuss Type of MCB ......................... in the UK Electrical Forum area at ElectriciansForums.net

Ok. Not soley for domestic but you know what I mean.

There is little in a domestic that requires a Type C.

Installing MCBs that trip at 5-10 times the current rather than 2-3 times should not be installed unless required.

Having a few LED downlights will not require a Type C.
 
In the days of predominate tungsten lighting I always fitted C 6A on lighting to prevent nuisance tripping from a failing lamp. B or C is mindset providing ADS is provided it is totally irrelevant.
 
I used to fit C type for the old toroid type wound transformers feeding several halogen downlights with individual outputs, apart from that always B.
 
Ok. Not soley for domestic but you know what I mean.

There is little in a domestic that requires a Type C.

Installing MCBs that trip at 5-10 times the current rather than 2-3 times should not be installed unless required.

Having a few LED downlights will not require a Type C.
I don't actually know what you mean.
 
I think a lot of it is down to availability too. We buy what the wholesalers have in for domestic stock. The wholesalers will be supplied with the devices that the manufacturers supply for domestic use.
This is generally a range of 6kA B curve breakers. You would have to specifically design for and request a C curve usually.

For instance Hager only do B curve mcbs in their 6kA range, and their reduced height RCBOs (aimed at consumer unit installation) at 6kA are all B curve.
 
There is no line of separation between a so called domestic protective device and a device for other purposes, it is mindset.
 
Back along with wire wound transformers d type was the one to use unless to completely dropped the loading of the circuit.
Don’t you remember walking into a a room and hearing the transformer start!
 
The product standard is EN60898 or EN61009 it is the type characteristics which define the intent.

I was meaning the difference between 60898 and 60947-2, but I think I may be getting a little lost in the argument.
My point was that if a manufacturer's 60898 offerings are solely B curve, that could be a reason why it has become mindset to install them as default.
 

Reply to Type of MCB ......................... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a small Consumer Unit fed from a 6 amp type B mcb to a 6 amp type B,it only feeds 1 light in a bin store . clearly we have no selectivity...
Replies
7
Views
603
I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
780
Hi all. Looking to refresh the MCB and RCCB (100A 30mA) units to my 20 year old Contactum P12/100N CU installed in my house. I have presently a...
Replies
2
Views
294
Hello everyone, How do you think reference method and type of wiring for flat twin and earth in non-metallic conduit will be : just C and B...
Replies
2
Views
223
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
494

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock