Discuss Type of MCB ......................... in the UK Electrical Forum area at ElectriciansForums.net

An MCB has two main functions:

a) To protect cables and accessories from overheating through overload. This is done by the thermal tripping mechanism of the MCB and follows the same curve for all types. Provided IB<In<Iz all is well and the cable will always be protected, because the characteristics of the cable and MCB are known and matched.

b) To protect cables and accessories from overheating, limit the dissipation of energy at a fault, and limit the duration of shock due to high touch-voltage, by disconnecting faults rapidly. This is done by the magnetic tripping mechanism, and the current threshold at which this takes over from the thermal mechanism depends on the MCB type. In effect, the value of I/In defines the point at which the MCB switches purpose from keeping the cables within ratings to clearing a possibly life-threatening shock fault or imminent fireball ASAP.

In a perfect world, whenever a fault occured, it would be a solid short-circuit of zero resistance that would dissipate no energy and allow a current of Uo/Zs to flow, hence trip an MCB of any permissible type. But in reality, faults are random in nature. Energy is often dissipated in destructive arcing and heating, and the current may not be as high as the Zs would suggest. Therefore, a curve that transitions to instantaneous tripping at a lower I/In may trip faster, reducing exposure to touch voltage and limiting energy dissipation at the fault. Under these conditions, a B-type may offer greater safety, provided it is compatible with the load, which for a mixed domestic load it usually will be.
 
An mcb has one function, to disconnect due to excess current by way of fault current or over current. The sole function is always an excess of current.
 
This is just a matter of semantics. There are two fundamentally different scenarios in which an MCB might react to 'excess current' that demand different sensitivity and speed. But in both cases, it is the excess current that triggers a tripping mechanism inside the MCB.
 
The product standard is EN60898 or EN61009 it is the type characteristics which define the intent.

MCB's that are built only to the standard EN60898 should not be used in an industrial environment.

Not really conducive to this thread but I felt I should point it out.

It's not a common issue as most MCBs are built to meet the requirments of both EN60898 and EN 60947-2 that latter being the requirement for industrial applications.
 
The only time I've needed to fit a type C was for a welding machine, pretty inductive loads can look like a momentary short on start up and cause it to trip. This was dedicated 16A supply, be wary that the max Zs values change (almost a half lower) for the whole circuit - from 2.73 to 1.37 Ohms. Be mindful of this when using for other connections (additional 13A sockets on the same circuit).
 
In any case, as already stated, ADS needs to be achieved whatever type you install.

Also, more of an issue, there are a lot of 61009 RCBO's in houses that are C type curve. Uo*cmin/Zs not high providing enough PEFC for the MCB part so then relying on the RCD part for of the unit for ADS under earth fault, this is ok.....but L-N shorts are covered by the MCB part only and mostly this isn't even being checked! (T=(K2*S2)/I2). Although often fine as cpc reduced compared to live conductors CSA, Calc should be insisted on if ADS under earth fault is only being achieved by RCD part of the RCBO.
 
Last edited:

Reply to Type of MCB ......................... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a small Consumer Unit fed from a 6 amp type B mcb to a 6 amp type B,it only feeds 1 light in a bin store . clearly we have no selectivity...
Replies
7
Views
595
I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
760
Hi all. Looking to refresh the MCB and RCCB (100A 30mA) units to my 20 year old Contactum P12/100N CU installed in my house. I have presently a...
Replies
2
Views
289
Hello everyone, How do you think reference method and type of wiring for flat twin and earth in non-metallic conduit will be : just C and B...
Replies
2
Views
212
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
486

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock