Notwithstanding the fact the pipe is plastic....

new boards still come with a earth bar inside, labelled, and there’s usually a “B” for bonding next to the numbered terminals for circuits.

saying that, if there is an MET, main earth terminal, then I’d use it.
It’s easier to test from, and you can visually check it without cover off board.
 
If I still had a metal gas pipe coming into my house and the dedicated 10 mm earth cable from the main earth terminal was needed near the meter what exactly would this earth cable be protecting me from ?
In simple terms....
Firstly it prevents the pipe inside your house becoming dangerous to touch due to it becoming live from a source outside your house. The current path will be via the low resistance bond making the pipe safe to touch.
Secondly if the pipe became live inside your house, it protects someone outside your house being able to receive a shock by touching the pipe while standing on real earth as the current path would again be through the low resistance bond.
(Touching an insulated but live pipe inside your house is not something I'd volunteer to do but with dry hands wearing shoes is certainly less dangerous)
 
When earthing gas and water service pipes do the 10mm earthing cables HAVE to come from the main earthing terminal (first tee) or can they come from a consumer unit that is connected to the main earthing terminal by a 16mm earth cable ?

What specifiacally do the relevant regulations say about this (my house was built in 2012) ?

I ask because Cadent recently changed the gas pipes in my street to plastic and they moved my gas meter nearer the road because the gas pressure was too low with the new thin pipes.

However they refused to earth the new copper gas pipe they installed inside my garage that connects my boilers to the new meter position.

They said the earth cable for the old meter position comes from a consumer unit after the first tee which doesn't comply with regulations and so they wouldn't earth the new copper gas pipe they had just installed.

Note there are three consumer units in my house each of which is connected to the main earthing terminal by 16mm earth cables which is why I have a main earthing terminal even though it's not directly used to earth the gas and water pipes.

On a wider note do you think Cadent are being reasonable or unreasonable as regards refusing to earth the new gas copper pipe in my garage ?
You aren't earthing the pipework, you are bonding them to ensure the pipework is at the same potential as the main earth conductor to your property, pedantic it maybe, but that is why they are called main bonding conductors. from the CU EARTH BUSBAR IMO
 
You aren't earthing the pipework, you are bonding them to ensure the pipework is at the same potential as the main earth conductor to your property, pedantic it maybe, but that is why they are called main bonding conductors. from the CU EARTH BUSBAR IMO

Indeed.
 

Reply to UK Main Earth Cable Source in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
896
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
3K
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
296
Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock