Hi,

this is a bit complicated.

We installed two separate underfloor heating system in our downstairs area.
One at 240V and according to the manufacturer at 11.9Amps. The other one also at 240V and 9.7Amps.

Because of the lack of space in the 200Amp panel, we connected them to two separate tandem breakers, each one at 2*15Amps. The panel is new and all electricians involved in this agree that it can handle tandems.

There are two thermostats one for each circuit. The thermostats can handle up to 15Amps, that's why we have two.

Here is what happens: Only one circuit will heat up! And it really depends which ones of the thermostats I crank up first.

My installer thinks it's because of the tandems. We checked and they are installed properly. Still he says it's because of the tandems (without providing further evidence).

We also talked to the underfloor heating provider. They said the tandems should be at least 20Amps. But my installer disagrees because the thermostat can only handle 15Amps each...

I was wondering what you guys think about this. Why could it be that tandems "generally" don't work for this type of installation or why 20Amps tandems might work?

Thanks
 
UK readers - the OP appears to be in the USA, perhaps Lancaster PA or CA, not Lancaster in Lancashire.
OP - this is mainly the UK section of the forum.

It seems to have been moved to the USA section

Are you saying that you fitted one tandem on each phase in the panel, and connected each heating zone from one side of one tandem to one side of the other tandem to get 240V? I'm not sure that meets code but let's wait for confirmation on that, it won't stop it working it's just about isolation safety.

Are the breakers tripping? If not, and both zones work OK independently, I can't see that the breakers have anything to do with the problem. There can be issues if your panel is packed with tandems running heating circuits as the heat dissipation in the breakers is more concentrated than with ordinary SP or DP breakers, but the problem manifests as premature tripping and you haven't said they're tripping. I can't see a problem with the breakers being 15A, especially if they are not tripping at all.

I think you would need to take some measurements. If one zone won't heat, where is the power actually getting to? Is there 240V leaving the breakers and is the thermostat closed i.e. voltage reaching all the way to the element? Actually as it's resistive heating elements it could be tested more safely with the circuit off using resistance tests, and the resistance of the element can be checked at a time when it refuses to heat. Without tests we'd just be guessing how the two zones are interacting. Is there any possibility that the wiring of the two thermostats and two elements has got badly muddled up in a j-box somewhere and the two are effectively in series?
 
Last edited:
UK readers - the OP appears to be in the USA, perhaps Lancaster PA or CA, not Lancaster in Lancashire.
OP - this is mainly the UK section of the forum.

It seems to have been moved to the USA section

Are you saying that you fitted one tandem on each phase in the panel, and connected each heating zone from one side of one tandem to one side of the other tandem to get 240V? I'm not sure that meets code but let's wait for confirmation on that, it won't stop it working it's just about isolation safety.

Are the breakers tripping? If not, and both zones work OK independently, I can't see that the breakers have anything to do with the problem. There can be issues if your panel is packed with tandems running heating circuits as the heat dissipation in the breakers is more concentrated than with ordinary SP or DP breakers, but the problem manifests as premature tripping and you haven't said they're tripping. I can't see a problem with the breakers being 15A, especially if they are not tripping at all.

I think you would need to take some measurements. If one zone won't heat, where is the power actually getting to? Is there 240V leaving the breakers and is the thermostat closed i.e. voltage reaching all the way to the element? Actually as it's resistive heating elements it could be tested more safely with the circuit off using resistance tests, and the resistance of the element can be checked at a time when it refuses to heat. Without tests we'd just be guessing how the two zones are interacting. Is there any possibility that the wiring of the two thermostats and two elements has got badly muddled up in a j-box somewhere and the two are effectively in series?
1) Indeed that's how we fitted the wires in the panel to get to 240V
2) no breakers are tripping ever.
3) we have a lot of tandems as the electrician put in a smaller panel than I wanted him to put (but I didn't pay enough attention...learning for next time)
4) we did these tests below and they all passed:
Test 1: Conductor resistance (required)
Test 2: Conductor and ground braid continuity (required)
Test 4: Thermostat Floor Temperature Sensor Test (required)
Test 3 "Insulation resistance (recommended)" wasn't done because the guy didn't have a megohmmeter.

Are there any other tests that you can think of?

5) there is absolutely the possibility that they messed the wires up. We have the thermostats next to each other and the heating floor wires coming from the same direction. If the wires were crossed at the thermostats however, would the system work at all?
 
Hi,

this is a bit complicated.

We installed two separate underfloor heating system in our downstairs area.
One at 240V and according to the manufacturer at 11.9Amps. The other one also at 240V and 9.7Amps.

Because of the lack of space in the 200Amp panel, we connected them to two separate tandem breakers, each one at 2*15Amps. The panel is new and all electricians involved in this agree that it can handle tandems.

There are two thermostats one for each circuit. The thermostats can handle up to 15Amps, that's why we have two.

Here is what happens: Only one circuit will heat up! And it really depends which ones of the thermostats I crank up first.

My installer thinks it's because of the tandems. We checked and they are installed properly. Still he says it's because of the tandems (without providing further evidence).

We also talked to the underfloor heating provider. They said the tandems should be at least 20Amps. But my installer disagrees because the thermostat can only handle 15Amps each...

I was wondering what you guys think about this. Why could it be that tandems "generally" don't work for this type of installation or why 20Amps tandems might work?

Thanks
The tandems will withstand the amperage that’s marked on the breaker. I’m my opinion you can use 20 amp tandem breakers. We are talking about 5 more amps so no problems. Don’t listen to your installer because the provider knows what it requires. I hate to say this but your electrician is wrong.
 

Reply to underfloor heating and tandem breakers in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
852
Hi. I'm installing a wet underfloor heating system in my own house. What would you recommend as the best smart control system? I can hardwire...
Replies
3
Views
639
m having a bit of an issue that is proving difficult to resolve. For 2 years I have been having no problems with my setup. I have a 3 zone house...
Replies
1
Views
1K
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K
I've done a significant amount of wiring in my previous work shop; but just moved to a new location. I have the need to wire up two 220v plugs...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock