I have a client with electic underfloor heating (two mats) one is fine the other shows an open circuit - anyone know how I can locate the break in the cable without digging up the whole floor?:confused:
 
@chloebear
Assuming you've started by looking for fixings into the floor and checked them for signs of stray voltage, if the mat is not buried too deep, then you could try with a "live cable detector" preferably one with adjustable sensitivity.

Start by putting a supply to one side of the mat, if it's not shorting out then it should present mains voltage at the open end, then try the other side to either confirm it or show up more than one break.
Be safe! well insulated shoes and gloves! or better still use the 110v side of a site transformer that way you are isolated from the mains.
 
You have no chance. there is a way to work out the distance of a fault if you know the approx run of a cable but to find the location of a fault on a heat mat would require more luck then skill (heat mats have elements that run back and forth so you would need to know which way they run and the distance they are spaced to even come close to the point of the break)....Sorry but taking up the tiles is the only option i can offer. Others may know a way!!!!!

Ash
 
Yeah, agree with ashrow....this isn't a straight run of cable but is likely to be a closely twisted run.

Assuming the mat worked at some previous point there must have been an incident to cause the break? Grandmother and eggs I know but have you looked around for any broken tiles or grout (indicating a tile has moved) or something fixed down (floor) or up (ceiling)?

The better news is that many mat manufacturers provide a repair kit once you've found the blighter.
 
The cable is in effect a heating element and cannot be repaired. Your only chance would be if the fault is in the tails connected to the mat. This is one of the big problems with electric under floor heating which is why most big jobs use wet systems.
 

Reply to Underfloor Heating in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

Similar Threads

Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K
m having a bit of an issue that is proving difficult to resolve. For 2 years I have been having no problems with my setup. I have a 3 zone house...
Replies
1
Views
1K
Hi, I'm getting renovations done to my home, including an existing extension which already has wet underfloor heating. We are moving a kitchen...
Replies
16
Views
4K
I have not had to do the wiring for a wet underfloor heating system before. I think I started a thread fairly recently and had some very good...
Replies
24
Views
2K
Hello Guys, I was wondering if any of you nice chaps could lend me some advice. So I have an open vented heating system with a 3 port valve...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock