S

skyline2500cc

A new supply has been installed by SSE and its a single phase TN-C-S in other words neutral and Earth combined at the cutout or point of supply.
Meter tails have been installed to a distribution board which feeds one circuit. From that distribution board we need to run a SWA conductor from an MCB, 600 meters underground to an outbuilding which will have another distribution board to feed additional circuits.
We have looked into the cost of a 3 core SWA copper cable and its between 4-5K. I was wondering as the earth and neutral are combined do the regulations permit you from running a 2 core i.e Live and Neutral and using the SWA or (CPC)
as the earth.
Look forward to any advice
:icon12:
Skyline2500cc
 
what size conductors in the SWA? generally armour is good for cpc up to 95mm or thereabouts.
 
Hi Telectric
Thanks for your response we are looking at 70mm2 CSA. The question I would like to know is there any technical, or regulatory reason why the SWA could not be used, saving us the expense of the third copper conductor.
Regards
Skyline2500cc
 
600 metres is a long run for an LV cable. I'd imagine that volt drop will be your biggest challenge.

With regard to earthing, you can always make the remote end a TT installation so you're not reliany on the TNCS earth.
 
Hi Telectric
Thanks for your response we are looking at 70mm2 CSA. The question I would like to know is there any technical, or regulatory reason why the SWA could not be used, saving us the expense of the third copper conductor.
Regards
Skyline2500cc

It is permitted, but you'll need to do all the necessary calculations to ensure it complies with BS7671. If you have any extraneous parts in the outbuilding you'll need to consider bonding them. You may be better to use TT, but the volt drop will still be a big factor to consider.
 
The armoring will only be suitable for the circuits CPC, not if this building needs any extraneous metalwork bonding.

Just be aware of your Zs for a circuit this long, in the past I have used enhanced conductive SWA, one armor strand in 5 was copper coated to get around it.
 

Reply to Underground SWA Cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
561
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
786
Hi, I'm looking for a bit of advice on a volt drop query we have in our office. I'll explain the scenario and I would really appreciate any...
Replies
3
Views
681
Just wanted to know which people use. My case. Client converting attached garage into new rooms. Consumer Unit has to move to accomodate this...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock