Discuss Understanding Volts and Amps!! in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,607
I'd like to understand a bit more about what actually gives you an electric shock. I think the more you understand something the safer you will be.

I have been taught that it is the current (amps) that gives you the shock, but this then confuses me with regard 12v equipment (lets say anything domestic - downlights for example using a transformer), as if the lights are 10W then:

Power = Voltage x Amps

10 = 12 x Amps

Amps = 10/12 = 0.83

If however the light were from the mains:

Amps = 10/230 = 0.04

So according to the maths a low voltage system uses more current and would be more dangerous as its amps that cause the shock. I know I'm missing something simple as this cant be right but I get a bit carried away with maths!

Could anyone explain this a little please?
 
You're right saying it's current that does the damage.

It's voltage that drives current through a given resistance, Ohm's Law.
So greater the voltage, greater the current, hence 12V is regarded as 'safe'.

In your lamp example, the 12V ones have a lower resistance than the 230V variety, hence larger current to give the same Power rating for both. P = IV.
 
I'd like to understand a bit more about what actually gives you an electric shock. I think the more you understand something the safer you will be.

I have been taught that it is the current (amps) that gives you the shock, but this then confuses me with regard 12v equipment (lets say anything domestic - downlights for example using a transformer), as if the lights are 10W then:

Power = Voltage x Amps

10 = 12 x Amps

Amps = 10/12 = 0.83

If however the light were from the mains:

Amps = 10/230 = 0.04

So according to the maths a low voltage system uses more current and would be more dangerous as its amps that cause the shock. I know I'm missing something simple as this cant be right but I get a bit carried away with maths!

Could anyone explain this a little please?

Human Body 1000 ohms

Voltage 11kv Current through body = 45.83 amp
Voltage 240v = 0.24 amps
Voltage 12v = 0.012 amps
 
My college teacher compared electricity to water flowing through a pipe.
The current is how much water there is and the voltage is the pressure behind it making it flow.
Just another simile type description to try and help you understand.

Dan
 
adding on to this, are you saying its cheaper to run 12v/50w lamp ,than 230v/50w lamp...?????????????????:rockon2:



Human Body 1000 ohms
?????????????
Voltage 11kv Current through body = 45.83 amp
Voltage 240v = 0.24 amps
Voltage 12v = 0.012 amps
 
I think I'm getting it! Its all to do with resistance!

At lower voltages your body has much greater resistance therefore less current will run through you.

Apparently at 25V the total body impedance of a hand to hand circuit for dry skin, large contact areas, 50 Hz AC currents would be roughly 3250 ohms.. so

current passing through you would be only 0.007A

Thankyou Chris and Archy for making me think of resistance! Brightspark2, wouldn't it be the other way around? Amps are the electrons (i.e the punch), volts the push, i.e how fast coming at you?
 
adding on to this, are you saying its cheaper to run 12v/50w lamp ,than 230v/50w lamp...?????????????????:rockon2:

No, 12V would use more amperes...

Brightspark2, wouldn't it be the other way around? Amps are the electrons (i.e the punch), volts the push, i.e how fast coming at you?

Nope, volts size of punch, amps is how fast its coming at you. Remember its not a fact just a similie, dont look into it too much lol...
 

Reply to Understanding Volts and Amps!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
1
Views
688
Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K
Why is this still a thing, just done a quick calculation with the TLC volt drop calculator and if its a non lighting circuit the recommended size...
Replies
3
Views
941

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock