Search the forum,

Discuss Unusual gas meter bonding in the UK Electrical Forum area at ElectriciansForums.net

newfutile

-
Esteemed
Arms
Supporter
Reaction score
389
3 gas meters bonded via a rod , I have not been in these properties
just thought I see what others think of this?
 

Attachments

  • 61424F51-9E3A-4143-93B4-53B2E1E56AFB.jpeg
    304.1 KB · Views: 33
stupidity. gas pipe is extraneous and already well connected to the mass of the earth. why add a rod?
 
what will the gas monkeys come up with next? plastic earth clamps in case the plastic service pipe is wet?
 
And if it was a TT installation and that was the means of earthing rod just there, then it’s still wrong, I reckon. The rod should be directly connect to the site MET and the bonding should go there as well. So at least 2 g/y going to MET.
 
3 gas meters bonded via a rod , I have not been in these properties
just thought I see what others think of this?
Is it bonding though? the wires go back to the stake not the MET I can see no main earth cable going to the MET from the stake either.
 

Reply to Unusual gas meter bonding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, it's been a while since I've been on, apologies. I am debating whether I need to replace the bonding to the gas meter. The meter is...
Replies
1
Views
350
I have an new set of circs here... Landlord in Cyprus EICR needed in empty flat. No credit on meter. Need power for Ze (TNCS) and RCD test at...
Replies
11
Views
504
New gas boiler install. Previously no gas in dwelling, water is plastic. So no bonding presently. No other work, boiler supply to use existing...
Replies
11
Views
281
Hi Guys Would I be correct in thinking an electric cable can be as close as 25mm to a gas meter ? (not that I'd ever be that close out of...
Replies
4
Views
813
Hi all, So my factory needs more power, currently 100A/3p (70KVA) => 400A/3p (200KVA) UKPN wont upgrade existing supply and are insisting on new...
Replies
1
Views
415

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock