Discuss Unvented Cylinder stats s-plan in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Spoony

-
Reaction score
0
A9E764E5-9999-4FAF-B265-55F1DE81B19B.jpeg Hi all,
Please can I get some help. I’m currently wiring up 20 unvented cylinders at the moment. They are all part of an S-plan which is fine. The problem I’m having is with the two in-built stats on the immersion tank. One stat is a high limit cut out stat and the other is an Adjustable.
I believe the high limit stat should be wired as normally closed but I’m not sure about the adjustable one. Should the adjustable stat be normally open or closed?
Stat documentation added

27800E8F-A6C1-45A0-8554-E13704317010.jpeg
 
Yeh I’ve wired them in series. High limit stat first. These two stats don’t have an internal link so I’ve wired them back to a joint box. The tanks haven’t been filled yet so the adjustable stat is clicking at 20 degrees (internal temp of empty tank). So just to confirm I want the circuit to flow until it hits its click. Not afterwards.
 
Yes, wired in series with the DHW control. This is essential to prevent the cylinder boiling in the event of a fault.

Thought you had to be G3 qualified to do this work?
 
Ahh, probably.
I’d still be concerned that our OP doesn’t know this basic detail of unvented cylinder wiring.
Not just one cylinder, but he’s installing 20.
 

Reply to Unvented Cylinder stats s-plan in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I had to wire in an extra 2 port valve today to protect a newly installed unvented cylinder (replacing the old gravity fed one) in a standard Y...
Replies
12
Views
2K
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
947
Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
437
I recently wired a heating system with a UFH8 manifold and an unvented cylinder.... easy. Well it threw up a few problems. Initially I had the...
Replies
3
Views
3K
I recently fitted a Heatmiser Neostat for a customer in their hall- to control their radiators throughout the house (70’s 4 bed medium sized...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock