We are having a few challenges with the energy assesment values for Domestic RHI properties - any one seen this yet.
5 Properties, all run through the full MCS Energy and Heat Loss calcs,
same 5 properties, EPC's using the RdSAP all give an energy requirement between 30 and 50% lower than the MCS calcs,
So which is right?
Based on actual consumption figures and old epc's done on some of the properties the MCS one is within 10%
The problem is that the RHI is based on the EPC figure.
So we have one property estimated to consume 47,000kWh a year yet the EPC says and therefore the RHI will only pay for 34,000kWh ..
Seems like we're not the only ones to be facing this challenge:
EPC Problems could wreck domestic RHI
the MCS MIS Document says "The Standard Assessment Procedure for dwellings is not designed to accurately determine the heating and domestic hot water energy requirements of real dwellings."
In a slight understatement even DECC publicly said : "We know RdSAP isn’t the most accurate way of estimating annual heating and hot water requirements"
With the RHI figure significantly below historic consumption levels, we are having difficulty achieving a +ve ROI , so some type of Renewable Energy just won't get a look in through the RHI, or the installtion owener will be significantly under-compensated - maybe that's DECC's idea? - Kill it off before it starts?
5 Properties, all run through the full MCS Energy and Heat Loss calcs,
same 5 properties, EPC's using the RdSAP all give an energy requirement between 30 and 50% lower than the MCS calcs,
So which is right?
Based on actual consumption figures and old epc's done on some of the properties the MCS one is within 10%
The problem is that the RHI is based on the EPC figure.
So we have one property estimated to consume 47,000kWh a year yet the EPC says and therefore the RHI will only pay for 34,000kWh ..
Seems like we're not the only ones to be facing this challenge:
EPC Problems could wreck domestic RHI
the MCS MIS Document says "The Standard Assessment Procedure for dwellings is not designed to accurately determine the heating and domestic hot water energy requirements of real dwellings."
In a slight understatement even DECC publicly said : "We know RdSAP isn’t the most accurate way of estimating annual heating and hot water requirements"
With the RHI figure significantly below historic consumption levels, we are having difficulty achieving a +ve ROI , so some type of Renewable Energy just won't get a look in through the RHI, or the installtion owener will be significantly under-compensated - maybe that's DECC's idea? - Kill it off before it starts?