Hi all,

I have seen somewhere recently that one particular brand of USB socket is good for 500v for IR testing, but I can't now remember where or which brand. Is this now the standard for these things? Has anyone come across any brands which are ok to do this on? Help appreciated...
 
It should also be noted that the electronic circuitry inside the SMPS could easily be damaged by a 500 V insulation test injected across it. Consequently the USB port may fail to function following a 500 V Line to Neutral insulation test.
 
BG USB sockets state on them that an IR test will give a reading above 10MΩ.
I cannot remember which test i.e. 500V or 250V and I am fairly sure it was not line to neutral.
 
Personally, I remove the sockets and bypass with wago connectors. I don’t like it but I do like the readings! I think these damn things should have an isolator built in (operated from the front with a screwdriver) that disconnects the electronics. Where’s a good BS standard when you need one!
 

Reply to USB sockets and IR testing help... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All Has anyone come across Earth Leakage on a usb Socket the appliance being plugged in is live
Replies
15
Views
435
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
328
Hello I have some decking lights which to be fair, have been nothing but pain in the bottom since they were installed. Moisture in the lens lamps...
Replies
10
Views
2K
Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Replies
13
Views
1K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
644

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock