Discuss Use of a plug in electronic timer with convector heater? in the UK Electrical Forum area at ElectriciansForums.net

dimmy

-
DIY
Reaction score
0
I have bought a Dimplex 1/2/kw convector freestanding electric heater which does not have a timer. In the manual it states "do not use with an external switching device such as a timer so as to avoid the potential hazard of the inadvertent resetting of the internal thermal safety cut out device". HOWEVER on all the plug in timers (i.e.TIMEGUARD TRT05) it says "can be used with convector heaters up to 3kw...so I am really confused!. Any advice gratefully received...thanks
 
The info on the timers merely indicates that they are electrically robust enough to switch that size of load and would be fine with a heater that has a manual-reset thermal cutout. The Dimplex heater apparently has a self-resetting thermal cutout that remains in the tripped position while power is present if the heater has overheated e.g. if the airflow if restricted, but resets when power is removed for a few minutes. Therefore, a timer that cycles the heater power on and off without human intervention could cause the cutout to reset and the heater to overheat repeatedly each time it switches on, if left unattended. Obviously they don't want an overheating situation to carry on relying on the cutout, but to be spotted and corrected.
 
Last edited:
ok thanks...I thought that might be the case. Although I would think most modern convector heaters have an auto thermal safety cut out rather than a manual one. Therefore I think the makers of the plug in timers should make it clear they are not suitable for appliances with auto cut out.....cheers!
 
ok thanks...I thought that might be the case. Although I would think most modern convector heaters have an auto thermal safety cut out rather than a manual one. Therefore I think the makers of the plug in timers should make it clear they are not suitable for appliances with auto cut out.....cheers!
Seems like it is covered by the instructions of the heater, can you imagine the size of the instruction manual for the timer if it detailed every item it is/isn't suitable for use with?
 

Reply to Use of a plug in electronic timer with convector heater? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

At some point in the next several months I need to look at heating for an "anti-vandal site office" used as store and occasional workshop, 3m x...
Replies
2
Views
1K
Hello, I wonder if anyone could advise on a repair of a convector heater which I am attempted. I am a complete DIY/electrics novice so simple...
Replies
9
Views
8K
I came across a small electric hot water heater under the sink with a moulded plug in my friend's rented flat. He's on economy 7, and wishes to...
Replies
1
Views
2K
L
We stayed in a caravan in the last few days which had this fixed air blown heater underneath a wardrobe. Inside the wardrobe the heater has a 13A...
Replies
12
Views
3K
Specialist
S
Hi. I am off grid, UK. There is no grid tie or connection and there is currently no potential for connection. Background: I use a Honda EU10i for...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top