Discuss Use of FP200. Will it get messed up by too much flexing? in the UK Electrical Forum area at ElectriciansForums.net

Spoon.
oh bloody hell, that shows how behind with stuff I am, blush.

So, do all connections of flexible cables now need a crimp on the end?

I.E....connecting an immersion heater with some buytle or other heat resistant cable needs to be crimped?

Cheers for the reply Spoon, it is another learning day at Chez Sym
 
Last edited by a moderator:
Spoon.
oh bloody hell, that shows how behind with stuff I am, blush.

So, do all connections of flexible cables now need a crimp on the end?

I.E....connecting an immersion heater with some buytle or other heat resistant cable needs to be crimped?

Cheers for the reply Spoon, it is another learning day at Chez Sym
you use bootlace ( otherwise known as ferrule) crimps where fine stranded cable is terminated in a screw terminal. this is the ensure that all the strands are in contact with the terminal, and no whiskers.
i use this crimp tool as it's self adjusting as regards size.
Crimper Plier Set 0.25-6.0mm Adjustable Ratchet Wire Crimping Cord Pin End Tool | eBay - https://www.ebay.co.uk/itm/Crimper-Plier-Set-0-25-6-0mm-Adjustable-Ratchet-Wire-Crimping-Cord-Pin-End-Tool/322994537589?_trkparms=aid%3D555018%26algo%3DPL.SIM%26ao%3D2%26asc%3D49138%26meid%3D583a79fc10cd4a9caffd1d14a8a2c113%26pid%3D100012%26rk%3D5%26rkt%3D12%26sd%3D153019091412%26itm%3D322994537589&_trksid=p2047675.c100012.m1985
 
Thanks Telectrix.
So am I right in saying that if the OP uses a flexible cable to wire out this barn conversion all connections would have to be crimped?

Yes, as stated above and elsewhere I am an idiot.

If this is the case then shallow metal switch boxes would have to be replaced with metal single socket boxes to accommodate for the depth taken up by the crimp when connecting a one-way switch?

Thanks for your time
Sym
 
Is boot-lacing twisting the strands of the flexible cables together?
Which is what I would do when connecting multiple flexes.

I assume he means fitting boot lace ferrules to the stripper ends of the flex, which is the correct way to terminate flex into screw terminals as it prevents the spread of the strands and stops the screw from cutting through the strands.
 
If this is the case then shallow metal switch boxes would have to be replaced with metal single socket boxes to accommodate for the depth taken up by the crimp when connecting a one-way switch?

Thanks for your time
Sym

Not necessarily because plain ferrules don’t extend any further back than the stripped end of the insulation, it’s only bootlace ferrules which have a plastic collar.
Either way it is very rare to see a 16mm box used these days as very few dimmers or decorative switches actually fit on them.
 
I love working with FP200 Gold - I find it a real pleasure to work with. It is fully approved by BASEC for commercial and residential installations. Because it has a continuous CPC sheath, its use is not restricted to normal wiring "safe zones", though common sense needs to be used. It is also ok for surface wiring without covering - though only white (I think) is OK for external routes without conduit or other cover due to UV issues.

FP200 Gold has a better material for the internal wire sheaths c.f. 'No-Burn Platinum' which uses neoprene (I think) and is easy to damage mechanically.

As an earlier post stated, best way to strip is to score carefully around with knife (you do not want to cut right through it) and then gently bend backwards and forwards and then the outer covering breaks free and can be easily slid off.

I see no need for a ferrule and you would have to abuse it quite a lot to damage the foil CPC layer - there is a normal CPC wire run alongside the foil layer.
 
still needs to be run in safe zones if buried, so peeps know it may be there.
 
I love working with FP200 Gold - I find it a real pleasure to work with. It is fully approved by BASEC for commercial and residential installations. Because it has a continuous CPC sheath, its use is not restricted to normal wiring "safe zones", though common sense needs to be used. It is also ok for surface wiring without covering - though only white (I think) is OK for external routes without conduit or other cover due to UV issues.

FP200 Gold has a better material for the internal wire sheaths c.f. 'No-Burn Platinum' which uses neoprene (I think) and is easy to damage mechanically.

As an earlier post stated, best way to strip is to score carefully around with knife (you do not want to cut right through it) and then gently bend backwards and forwards and then the outer covering breaks free and can be easily slid off.

I see no need for a ferrule and you would have to abuse it quite a lot to damage the foil CPC layer - there is a normal CPC wire run alongside the foil layer.
Think the Foil you talk of is a scree, not a cpc.
 
I love working with FP200 Gold - I find it a real pleasure to work with. It is fully approved by BASEC for commercial and residential installations. Because it has a continuous CPC sheath, its use is not restricted to normal wiring "safe zones", though common sense needs to be used. It is also ok for surface wiring without covering - though only white (I think) is OK for external routes without conduit or other cover due to UV issues.

FP200 Gold has a better material for the internal wire sheaths c.f. 'No-Burn Platinum' which uses neoprene (I think) and is easy to damage mechanically.

As an earlier post stated, best way to strip is to score carefully around with knife (you do not want to cut right through it) and then gently bend backwards and forwards and then the outer covering breaks free and can be easily slid off.

I see no need for a ferrule and you would have to abuse it quite a lot to damage the foil CPC layer - there is a normal CPC wire run alongside the foil layer.
Think the Foil you talk of is a screen, not a cpc.
 
It is fully approved by BASEC for commercial and residential installations. Because it has a continuous CPC sheath, its use is not restricted to normal wiring "safe zones", though common sense needs to be used. It is also ok for surface wiring without covering - though only white (I think) is OK for external routes without conduit or other cover due to UV issues.

FP200 Gold has a better material for the internal wire sheaths c.f. 'No-Burn Platinum' which uses neoprene (I think) and is easy to damage mechanically.

It is not fully approved by BASEC for commercial and residential applications, that’s not how BASEC approval works. BASEC independently test and approve the cable to confirm that it meets applicable British standards, the don’t make mention of what it should be used for or where it should be used.
The BASEC approval for FP200 gold (freely available on the FP website) merely shows that it meets the standards for fire resistant screened cable.

The sheath is not a CPC, there is an aluminium foil screen bonded to the inside of the sheath which is in contact with the bare CPC inside.
 
It is not fully approved by BASEC for commercial and residential applications, that’s not how BASEC approval works. BASEC independently test and approve the cable to confirm that it meets applicable British standards, the don’t make mention of what it should be used for or where it should be used.
The BASEC approval for FP200 gold (freely available on the FP website) merely shows that it meets the standards for fire resistant screened cable.

The sheath is not a CPC, there is an aluminium foil screen bonded to the inside of the sheath which is in contact with the bare CPC inside.

I have a letter from Dr Jeremy Hodge, then CEO of BASEC, written about ten years ago, confirming to me that FP200 Gold is fully approved for general wiring use in homes and commercial premises. I have also discussed the issue with him several times. The foil is an extension to the CPC (I agree it is not the actual CPC) that has been fully tested to trip a 100 mA RCD (I think it is OK up to about 1 A) if the cable is penetrated by a nail or screw and the phase conductor is touched by the screw. So, as long as the installation is RCD protected, the places the cable can be run are reasonably unrestricted. The reason CY and SY and similar braided cables do not comply is that you cannot guarantee that the nail will make a good enough contaict with the braid as there are 'holes' in the braid knitting.

In November 2017, Dr Jeremy Hodge stepped down as CEO but remains in the business as Technical Director to enhance BASEC’s technical leadership in cable testing and certification, supporting Tony. Jeremy also remains as a Board Director of British Approval Services for Cables.
 
I have a letter from Dr Jeremy Hodge, then CEO of BASEC, written about ten years ago, confirming to me that FP200 Gold is fully approved for general wiring use in homes and commercial premises. I have also discussed the issue with him several times. The foil is an extension to the CPC (I agree it is not the actual CPC) that has been fully tested to trip a 100 mA RCD (I think it is OK up to about 1 A) if the cable is penetrated by a nail or screw and the phase conductor is touched by the screw. So, as long as the installation is RCD protected, the places the cable can be run are reasonably unrestricted. The reason CY and SY and similar braided cables do not comply is that you cannot guarantee that the nail will make a good enough contaict with the braid as there are 'holes' in the braid knitting.

In November 2017, Dr Jeremy Hodge stepped down as CEO but remains in the business as Technical Director to enhance BASEC’s technical leadership in cable testing and certification, supporting Tony. Jeremy also remains as a Board Director of British Approval Services for Cables.
It's impossible for the foil to be classed as an extension of the cpc, it is not connected to the earthing system in any way, other than contact by touch, not by connection, respectfully suggest that Dr Hodge is typical of many Scientists who take thing literally, and don't see the practical side of things.
FP200 Gold Fire Resistant Cable from Prysmian - https://www.fpcables.co.uk/FP200.html
Further information
Prysmian FP200 Cable - http://www.fpcables.com/prysmian-fp-cables/prysmian-fp200-cable/
Personally I would not use FP for anything other that what it is intended for.
 
Last edited:
If a cable complies to bs 8436 it can be non rcd protected and installed out of safe zones.

I’m not sure if fp200 gold meets that certain standard ie I doubt it.
 

Reply to Use of FP200. Will it get messed up by too much flexing? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I'd like to replace some MR16 halogen fittings on an exposed wooden beam to new GU10 fittings which I will be fitting led lamps into. The...
Replies
2
Views
1K
Getting desperate to clear my small garage, and I have a bit of old red/black T&E. I used a few bits to add a socket or two in my flat and a...
Replies
5
Views
1K
Hello! My electrical utility has decided to take our power away - occasionally - to prevent fires. So I have ordered a modest backup...
Replies
22
Views
9K
T
This week, I finally decided to get on with rejuvenating the supply to my garage. This was in place when we moved in and, in all honesty (and on...
Replies
11
Views
2K
Engineer54
E

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock