- Reaction score
- 25,517
There is a fair few on EBay.
Telford Electronics
www.telford-electronics.co.uk
Discuss Using conduit as a CPC in the UK Electrical Forum area at ElectriciansForums.net
Right, sorry, the Megger PAT101, I didn't know.There is a fair few on EBay.
Telford Electronics
www.telford-electronics.co.uk
Sorry I should have put PAT101. A while back we had some suspect IEC leads on some IT equipment, the bond was far higher than expected 0.30 and above. We took one outside and bond tested it until the cable went all floppy and took the earth out, there were about three tiny strands of copper on a cable claimed to be 3×1.0.Right, sorry, the Megger PAT101, I didn't know.
A useful thing to think about, IMHO.
I use my DLRO for much more than containment testing.
Motors, connections, earthing and bonding wiring.
The high current high accuracy, DLRO10HD, will give 0.1 micro ohm resolution at the 25 milli Ohm range.
Testing continuity at 25A feels much more effective and serious, but how many have actually discovered a problem by testing at this current, that would not have been found at a lower current. E.g. the IEC leads mentioned by @westward10 revealed themselves to a resistance test, before they gave out on a high current test. I am struggling to recall a genuine case of 'termination hanging on by a few strands' located on test and not by visual, which is a situation we often cite to justify the 25A test.
I once found an earth fault loop fault with a high current loop impedance tester rather than one of the modulated soft testers we use these days to avoid tripping RCDs.Testing continuity at 25A feels much more effective and serious, but how many have actually discovered a problem by testing at this current, that would not have been found at a lower current. E.g. the IEC leads mentioned by @westward10 revealed themselves to a resistance test, before they gave out on a high current test. I am struggling to recall a genuine case of 'termination hanging on by a few strands' located on test and not by visual, which is a situation we often cite
Crikey!That put mains voltage / 10 Ohms down the loop test wiring.
The old Robin separates are the ones that do this.Crikey!
I always assumed they had some transformer so it would be tens of volts at most and leakage inductance or whatever as current limit, like old fashioned lead-acid chargers.
Yes I still use a Robin makes the young lads jump when the leads crack on the terminals plus no batteries to go flat.The old Robin separates are the ones that do this.
Not sure what model mine is.
Reply to Using conduit as a CPC in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.