Went to carry out condition report on a flat. There is no earth cables from fuseboard to first point . The installation is over 30 years old and other contractors have just added twin and earth under floors/walls. R1+r2 values seem to be high aswel. Zs is not so bad and is within allowed time.main bonding to gas is 2.5 single earth and main earth from pyro cable is 6mm. The tenant and i could not find the main water supply to see if it was earthed. No isolators for equiptment in kitchen. Socket wired from cooker circuit in 2.5mm t&e on 32amp breaker. Cooker is wired in 6mmt&e.earths not connected at light switches and they are using metal plate switches.
i was goin to advise arewire wat are your thoughts?
Is the conduit allowed to be used as an earth or do you need a earth cable installed?
 
Of course Metal conduit is allowed to be the CPC for whatever circuits are enclosed in the system. The only time you should need to include a separate CPC conductor in a well installed conduit system, is if and when the conduit is breaking down due to corrosion...

You obviously need to upgrade the bonding conductors to the service pipes!! Maybe also upgrade the flying lead off the MICC supply cable to a 10mm...

As for rewiring the system, that depends on the condition of the installed wiring?? The T&E wiring was probably installed for placement of extra/additional socket outlets etc, that the original conduit system didn't cover!!
 
As stated the r1&r2 value is very high and the conduit is behind walls cupboards etc. this leads me to think there is some corrosion on conduit.
what about isolators for appliances in kitchen, bathroom fan etc do they have to have isolators. Also the 2.5 comin off 6mm on a 32amp breaker
cheers for the advise
 

Reply to Using conduit as earth. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Replies
0
Views
529
This question has probably been asked several time but things change. The house I'm living in now was built in the 1960's and has a ring main...
Replies
15
Views
867
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
524
Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin...
Replies
14
Views
1K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
841

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock