- Reaction score
- 49
is it dangerous to use the cpc in a twin / earth cable? I know it's not safe in case someone else thinks it's still an earth but is that the only reason?
Discuss Using cpc as neutral in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Might not be the same csa as the Phase conductor, not insulated over the entire length, what are you using as the cpc if you bodge the job by using it as the N, IT'S WRONG and against the Regulations, nothing else springs to mind other than it's Muppetry to do it.is it dangerous to use the cpc in a twin / earth cable? I know it's not safe in case someone else thinks it's still an earth but is that the only reason?
A bad joke at that.This has to be a joke
Commonly these are from a new member with a blocked profile .
Commonly these are from a new member with a blocked profile .
Cpc has to be present at every termination but in fact you can get it from wherever you like.Well .......... each cable should have a continuous CPC from the CU - can't remember the reg no.
Why is the profile blocked? has he something to hide? very odd.Commonly these are from a new member with a blocked profile .
Same applies to any conductor that isn't identified correctly but that would show up pretty quickly in testing. The main issue is the lack of insulation and the requirement to get an earth to every termination.is it dangerous to use the cpc in a twin / earth cable? I know it's not safe in case someone else thinks it's still an earth but is that the only reason?
Hi - not to joust, but not a good idea imho and may be prohibited by 514.4.2 .You can even oversleeve a green and yellow insulated core with brown in a multi core cable and that still complies with the regs
Agree it's a terrible idea when designing from scratchs but i don't agree it's dangerous and it would be picked up straight away by anyone working on the circuit.Hi - not to joust, but not a good idea imho and may be prohibited by 514.4.2 .
Cpc has to be present at every termination but in fact you can get it from wherever you like.
You can even oversleeve a green and yellow insulated core with brown in a multi core cable and that still complies with the regs. But you'd only do that if you were struggling to avoid a lot of redecorating!
The bare cpc is not insulated that would be your main problem.
MODs... Is this 'blocked profile' a glitch as the last member who had this said they hadn't changed anything?
No offence, unfortunately i can't do any more detailed explanation at that point! But i was addressing a part of your post not your usual excellent standards!So you've given me a disagree ............ hum
Reading the OP between the lines I imagine he wants to use the CPC as SL or similar .............. hence my reply.
Can't really what there is to discus John, you shouldn't use the cpc as a live conductor under any circumstances.No offence, unfortunately i can't do any more detailed explanation at that point! But i was addressing a part of your post not your usual excellent standards!
I do think that when people are asking this kind of question, we should be precise about why it's not allowed, and appeal to both the regs and to common sense specifically where appropriate.i think a lot of things that are uncommon in domestic are actually within the regs, and sometimes the boundary between what is allowed and what isn't seems to defy common sense, but as long as we discuss properly we will help everyone to learn something new.
Shouldn't according to what reason though? My point is try to be specific. If this was an eicr you can't just code things because it's not common practice.Can't really what there is to discus John, you shouldn't use the cpc as a live conductor under any circumstances.
So what would you use as the cpc in your scenario? and can you say which Regulation says that doing what you suggest complies with BS7671.In a t&e yes as i said because of the lack of insulation, however under the regs you can identify the green and yellow insulated conductor in a multi core cable as neutral or line by over sleeving.
Making sweeping statements about how you shouldn't do it isn't really helping anyone to learn something.
There's no need to have a cpc in every cable, you just need it available at every termination.So what would you use as the cpc in your scenario? and can you say which Regulation says that doing what you suggest complies with BS7671.
Shouldn't according to what reason though? My point is try to be specific. If this was an eicr you can't just code things because it's not common practice.
In a t&e yes as i said definitely not allowed because of the lack of insulation, however under the regs you can identify the green and yellow insulated conductor in a multi core cable as neutral or line by over sleeving.
Making sweeping statements about how you shouldn't do it isn't really helping anyone to learn something.
There's no need to have a cpc in every cable, you just need it available at every termination.
Yes please would be interesting, just a point how are you going to have a cpc at every termination if you don't as you say, need a cpc in every cable, and why would you use a cable with an earth core if you didn't need it? seems very counter productive in my book, are you sure you are not misreading/misunderstanding the regulations, still if you get hold of your copy and quote the Reg number we can all have a look.There's no need to have a cpc in every cable, you just need it available at every termination.
And the reg mentioned earlier covers over sleeving. You can identify any cable by over sleeving, the only restriction is you can't use green yellow identificationide anything other than cpc and you can't use over sleeving to identify a green yellow insulated single.
Don't have access to the regs right now but i can look later if necessary
514-03-02 - Every core of a cable shall be identifiable at its terminations and preferably throughout its length.can you say which Regulation says that doing what you suggest complies with BS7671.
Or multi core cable EitherGot to be a wind up,if he’s considering doing it to T&E I can’t imagine he’s used many single core cables ever anyway......
514-03-02 - Every core of a cable shall be identifiable at its terminations and preferably throughout its length.
So brown sleeving at the terminations would comply, although not be preferable
411.3.1.1 - A cpc shall be run to and terminated at each point in wiring and at each accessory
So as long as one cable that has a cpc arrives at the accessory you're ok
Fair enough but i feel having stated at least 3 times that it's not acceptable in t&e due to lack of insulation and been very specific about when it isn't an is allowed and for what reason, I'm actually quite disappointed that members i respect on here are throwing around disagrees without explanation beyond that it's shouldn't be allowed.I’ve given you a disagree on the basis that op asks about using the cpc as a live conductor
Fair enough but i feel having stated at least 3 times that it's not acceptable in t&e due to lack of insulation and been very specific about when it isn't an is allowed and for what reason, I'm actually quite disappointed that members i respect on here are throwing around disagrees without explanation beyond that it's shouldn't be allowed.
If you read the op carefully you will note he is trying to learn and he's asking for exactly which reasons it is not allowed, i didn't take away from that that he's planning to do it. Let's try to be constructive and learn something, if the op wants to do something dangerous then that's up to him, we are here to help, right?
Hope that came across ok, I'm not trying to start a disagreement i just think i only learn something from people i disagree with (if they are also happy to discuss)
Happy Monday (just to try to relax the mood
Ok fair enough I'm not the thread police so maybe the op broke the rules.Posters need to learn to post better threads and answer questions
For a non spark you seem to be going out of your way to pass people off.....
Hi - I'm struggling to think of installing a circuit without a cpc. Some have been installed historically, but I don't think that's been since the '60s. As I've started to practice for the regs exam ( ) the two regs I could find that seem relevant are 543.6.1 and 543.2.9 .There's no need to have a cpc in every cable, you just need it available at every termination.
Well saidShouldn't according to what reason though? My point is try to be specific. If this was an eicr you can't just code things because it's not common practice.
In a t&e yes as i said definitely not allowed because of the lack of insulation, however under the regs you can identify the green and yellow insulated conductor in a multi core cable as neutral or line by over sleeving.
Making sweeping statements about how you shouldn't do it isn't really helping anyone to learn something.
Thanks for the regs help! I can't think of a circuit without a cpc either, that would certainly not comply and i have not suggested it.I'm struggling to think of installing a circuit without a cpc
"Where overcurrent protective devices are used for fault protection, the protective conductor shall be be incorporated into the same wiring system as the live conductors or in their immediate proximity."the two regs I could find that seem relevant are 543.6.1 and 543.2.9
Thanks for the regs help! I can't think of a circuit without a cpc either, that would certainly not comply and i have not suggested it.
"Where overcurrent protective devices are used for fault protection, the protective conductor shall be be incorporated into the same wiring system as the live conductors or in their immediate proximity."
Same wiring system, but not necessarily the same cable, as i understand it.
The latter reg is talking about the special case of rings which are not under discussion but it states that the cpc should also be a ring.
Agree, that's basically what i meant when i was saying each cable didn't have to have a cpc as long as there was one available at every termination.Same wiring system does not necesarilly mean the same cable,
Sorry, i didn't mean to, as far as i can see from rereading my posts every single one was either addressing the question the op originally posted or attempting to clarify information provided by others, together with informative examples for further clarification.You did bring up quite a few points yourself which were not under discussion.
Thanks for the regs help! I can't think of a circuit without a cpc either, that would certainly not comply and i have not suggested it.
"Where overcurrent protective devices are used for fault protection, the protective conductor shall be be incorporated into the same wiring system as the live conductors or in their immediate proximity."
Same wiring system, but not necessarily the same cable, as i understand it.
The latter reg is talking about the special case of rings which are not under discussion but it states that the cpc should also be a ring.
There are reasons we work to a standard, primarily for safety.No offence, unfortunately i can't do any more detailed explanation at that point! But i was addressing a part of your post not your usual excellent standards!
I do think that when people are asking this kind of question, we should be precise about why it's not allowed, and appeal to both the regs and to common sense specifically where appropriate.i think a lot of things that are uncommon in domestic are actually within the regs, and sometimes the boundary between what is allowed and what isn't seems to defy common sense, but as long as we discuss properly we will help everyone to learn something new.
Interesting didn't think about that re wiring systems:, so if two 3 core flexes routed together you could do it in one of them but not if they went via different routes? Or is that only if they are in the same containment rather than being sheathed?‘Or Immediate proximity’ I read as 6491 singles in conduit or trunking taking the same complete route as both or all lives. This is in order to terminate at each accessory.
I meant strict in the mathematical sense of more tightly defined, not in the sense that i disagreed with it.@johnduffell you call it strict - I call it safe, as all installations should be.
We all need to sleep at night and installing safely to regulations, that are set in place for a reason, make my pillow feel like a cloud!
Hi - I'm struggling to think of installing a circuit without a cpc. Some have been installed historically, but I don't think that's been since the '60s. As I've started to practice for the regs exam ( ) the two regs I could find that seem relevant are 543.6.1 and 543.2.9 .
Not so long ago I was wiring up an underfloor heating system. The controls for the heating were all downstairs, along with domestic hot water controls. The zone valves, along with the water tank and gas boiler were all in the loft. To complicate things, there was also a solar thermal input and a 'warm loop' system. I had a twin n earth cable feeding the system and supplying a large junction box with its cpc. I also had two 5 core flex going up to the JB in the loft. Therefore, I had two green/yellow cores which were not required as a cpc. I did need to use one of these as a live conductor and oversleeved it at each end accordingly. Isn't this an example of when an unused cpc is legitimately used as a live conductor?
Reply to Using cpc as neutral in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net