Here's quick question...

Can I sleeve a green & yellow flex conductor with brown or blue to use it as a switched live or neutral?

I'm looking at a situation where I do not need the CPC connection (the timer switch I'm connecting to is class 2 insulated) but I do need live, neutral and switched live. So I'm wondering if I can use 3 core flex (so that the conductors are all insulated within the outer sheath, unlike T&E) and put a brown sleeve on the G/Y to use it as the switched live.

Thanks for your help, and sorry if this has been answered many times before!
 
Here's quick question...

Can I sleeve a green & yellow flex conductor with brown or blue to use it as a switched live or neutral?

I'm looking at a situation where I do not need the CPC connection (the timer switch I'm connecting to is class 2 insulated) but I do need live, neutral and switched live. So I'm wondering if I can use 3 core flex (so that the conductors are all insulated within the outer sheath, unlike T&E) and put a brown sleeve on the G/Y to use it as the switched live.

Thanks for your help, and sorry if this has been answered many times before!

Personally I don't like the idea!
 
It's in the NIC EIC ( So this may be one of their, well it's in our fictitious rule book etc) snags and solutions and if memory serves it is exceptable if the run is totally visible. Personally would never do it.
 
Last edited by a moderator:
I'm sure the regs state CPC (green & yellow) must NEVER be over sleeved or used for anything but CPC / Earth......

I'll try and located said reg
 
Last edited:
I will stand up to be shot at. I am certain that it does say somewhere in BS7671 that Green or Green and yellow are only to be used to identify earthing and bonding connections and must not be used for any other purpose. Or words to that effect. I am so sure that i would put money on it.

Cheers.........Howard
 
ttereg 514.4.2

green and yellow shall be used exclusively for identification of a protective conductor and this combination shall not be used for any other purpose.
 
Here's quick question...

Can I sleeve a green & yellow flex conductor with brown or blue to use it as a switched live or neutral?

I'm looking at a situation where I do not need the CPC connection (the timer switch I'm connecting to is class 2 insulated) but I do need live, neutral and switched live. So I'm wondering if I can use 3 core flex (so that the conductors are all insulated within the outer sheath, unlike T&E) and put a brown sleeve on the G/Y to use it as the switched live.

Thanks for your help, and sorry if this has been answered many times before!
For this type of work you should use a 3 core cable. In T&E the cross section of the earth isn't the same as the lives; so earth shouldn't be used as permanent live. Just my opinion.
 
Yes the green and yellow should only be used as a earth conductor but if you sleeve it with another colour ie brown/blue not a problem this can not be done with twin and earth cable. regs state green and yellow should only be used for
earth conductor this is correct but you have sleeved it its now not a earth conductor.
its no different than sleeving say a blue switch wire with brown sleeve or the black of a 3 core armoured yellow and green sleeve/tape.but after saying all that the flex you are using in that situation should still carry a earth.
 
Yes the green and yellow should only be used as a earth conductor but if you sleeve it with another colour ie brown/blue not a problem this can not be done with twin and earth cable. regs state green and yellow should only be used for
earth conductor this is correct but you have sleeved it its now not a earth conductor.
its no different than sleeving say a blue switch wire with brown sleeve or the black of a 3 core armoured yellow and green sleeve/tape.but after saying all that the flex you are using in that situation should still carry a earth.

doesnt matter mate not permitted in regs ,cpc's on cable TWE or #flex should never be used as a live conductor simples read back on some of the posts
 
For this type of work you should use a 3 core cable. In T&E the cross section of the earth isn't the same as the lives; so earth shouldn't be used as permanent live. Just my opinion.
use a 4 core so that any future modifications that may require an earth are then provided , i always make a earth available for that exact reason not connected but there
 
...and what if someone taps into the cable in the future and sees the section thats not sleeved, but still green and yellow? Might get a shock!
 
Thanks all for your comments on my original post - as a one person operation this is a very useful resource to get others' opinions.

With reference to some of the comments, I knew there were more issues with T&E because of the smaller conductor size of the CPC and that it is uninsulated inside the outer sheath.

Neither of those applies to flex though which is why it occurred to me that it might be possible to 're-label' the green/yellow, but you've pointed me to the regs which say no, so that's that!

Thanks again.
 
The restriction against using G/Y as anything other than a CPC/earth, only applies to single core cables, here is an excerpt from 514.4.2: "Single core cables that are coloured green-and yellow throughout their length shall only be used as a protective conductor and shall not be over-marked at their terminations, except as permitted by Regulation 514.4.3."
Whith multicore cables such as flex, or SWA, it is allowed to oversleeve the exposed core another colour.
 

Reply to Using Green/Yellow not as CPC in the Australia area at ElectriciansForums.net

Similar Threads

I see they're introducing a new type of flat twin cable with a sheathed CPC. In my location there's no requirement to sleeve CPC/bonding...
Replies
21
Views
2K
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
499
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K
Hello, I'm swapping my extractor fan in the UK and I have bought a Turkish extractor fan stupidly and the connections you can see in the picture...
Replies
1
Views
345
Wouldn't normally note this as an observation on a report but feel I need to. The way the building has been wired is all circuits on L1 have been...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock