This installation has a very old DNO metal fuse box with a hinged lid, which may or may not open in one piece.
The DNO's meter feeds 2 x 63A MCB's in a 2 slot CU.

Can I feed a Henley block with both line connections from the 2x63A MCB's, thus using it as a local isolation switch?
The 80-100A DNO fuse should blow before the combined MCB's operate, assuming the current is split equally, which is should be.
The Henley block can then feed a normal CU.

Bit unconventional, but trying to think out of the box whilst waiting for DNO to fit local isolation?
 
no way mate. suppose you had to isolate the circuit and switched 1 MCB off. circuit would still be energised through the other 1.
 
An MCB and an isolator are two physically different things. Most MCB's aren't rated as isolators.
 
Some possibles

Each mcb would need to be linked physically at the very least so they both drop out
You will have a combined rating equivelent to a 126 amp mcb
Each tail would be too small for the combined mcb rating
The mcbs would have a higher rating than the enclosure
It wouldn't be a double pole isolator
Probably the mcbs wouldn't survive a prospective short circuit current


Its probably best staying as just a thought :)

Its so much easier an option, just to dump the mcbs and fit an isolator, then switch the neutral as welll,no dno no hastle no problem
 
Last edited:
True mate if you wish to use it as in reg 537.1.4, for both a TN and TT system.

In a TN system an isolator only need to switch the LINE conductor if the neutral is deemd to be conected to a reliable earth at a suitably low impedance.

537.1.4 A main switch .. shall interrupt both live conductors of a single-phase supply
 

Reply to Using MCB's in parallel to give local isolation in the Australia area at ElectriciansForums.net

Similar Threads

I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
Replies
9
Views
5K
Hello all. 17th edition sparky here, but not been on site for the last 3/4 years (had a bit of an accident). Just bought a house with a 16mm 3...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock