Discuss Using Type D MCB for discrimination in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
88
I've just been on phone with Hager designing domestic distribution board design. Engineer advised using Type D 63A in distribution board supplying CU to give better discrimination. Looking at tables anything over 10A on CU might also trip Type D, but it does give a better chance.
So I need to make sure this is okay, I've found reference to 16th edition Regulation 413-02-08. But this has been moved in 17th edition and I can't find anything. Has anyone got any pointers and thoughts about using Type D breakers for domestic distribution panel?
 
Well using a type D mcb @ 63 amp would give a maximum zs of 0.35 ohms for a maximum disconnection time of 5 seconds being a distribution circuit, that’s without the 0.8 correction factor
Typically it’s very difficult to achieve your zs values using type D for lower rated mcbs using 0.4 seconds as their maximum disconnection times as the typical zs values are Uo x cmin/ In x 20

I would suggest using a bs 88 fuse for protection of your submain tho.
 
Its an interesting thread this ...................... there are so many submains in service supplied from standard type B MCB's .............. including one in my shed. :)

But if this is protection from the DNO fuse to the CU what do you do if the DNO fuse is 60A
 
Its an interesting thread this ...................... there are so many submains in service supplied from standard type B MCB's .............. including one in my shed. :)

But if this is protection from the DNO fuse to the CU what do you do if the DNO fuse is 60A
One of our customers has some telecoms modules with no discrimination. Had a 16 amp C type trip out and it also took out the distribution circuit in the generator room and the main incoming 160 amp MCCB.

Luckily the DNO 200 amp fuses never broke a sweat...
 
You are only going to achieve partial discrimination at the very best. It's just carp design from the onset. Multiple 60898's in series for a supply to a shed isn't really going to be a drama if it trips and takes out the upfront Circuit breaker. Put the same situation in a factory where taking out the upfront circuit breaker could lead to loss of production and consequently loss of thousands of pounds...then you have a real problem. Also worth considering that due to lack of discrimination you may not be able to minimise disruption in the event of a fault.
 
Its an interesting thread this ...................... there are so many submains in service supplied from standard type B MCB's .............. including one in my shed. :)

But if this is protection from the DNO fuse to the CU what do you do if the DNO fuse is 60A
pick a 100A one up from the wholesalers and put it in place of the 60A one...play dumb if the DNO ask anything :eek::D
 
Well using a type D mcb @ 63 amp would give a maximum zs of 0.35 ohms for a maximum disconnection time of 5 seconds being a distribution circuit, that’s without the 0.8 correction factor
Typically it’s very difficult to achieve your zs values using type D for lower rated mcbs using 0.4 seconds as their maximum disconnection times as the typical zs values are Uo x cmin/ In x 20

I would suggest using a bs 88 fuse for protection of your submain tho.

That's the answer I was looking for...... well actually not what I wanted but that kills this option dead. Looking at old EIC Zs up to 0.9, typically around 0.6
 
Fuse holder module??

You only get standard size fuseholders up to 32A any bigger and its a double module, so the busbar won't fit.

What not individual switch fuses?
 

Reply to Using Type D MCB for discrimination in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi guys, Rewired a unit where they make dentures, builder today has asked to install 16a commando socket with isolator (no problem) however...
Replies
23
Views
3K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
679
Probably more of a maths problem than anything else / managing to confuse myself. I have been asked to look at energy consumption of some...
Replies
7
Views
534
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
Hi, I've got to put in an additional consumer unit into quite a large property and rather than daisy chaining them back to a single MCB in the...
Replies
8
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock