They sell them in Senate's £39 ,they were giving them away for free when you buy 2 consumer units, don't know if deal is still on though.
 
I made my own adapter using an extension socket connected to three 4mm test leads that I plug into my multifunction tester. I can do insulation resistance continuity polarity which are the basic tests, and though 200mA is called a soft test, if its good enough for an installation then why not for an appliance?

The standard for pat testing allows the use of other instruments, although it says that a pat tester may be easier to use. my adapter cost me a few pounds and has paid me well. I also made a 110v and 230v bayonet adapter that plug into my meter. Why pay for and carry two testers when one can do everything?

I have asked ECA, NICEIC, NAPIT and they all say that my method is acceptable, provided that I keep my tester calibrated with the adapters provided for examination when I send it in
 
earth continuity/ imsulation resistance/ fuctional checks is the minimum and i for sure will be using one of these devices too..
 
I have used pat testers for many years starting with older machines where you had to record the results on a paper carbon duplicating sheet and i can assure you that unless you are only gonna do a few tests for the odd customer then the best way to go is with a modern pat tester as the speed efficiency and ability to download straight into a report generating database program is well well worth the cash or perhaps find a good pat guy in your area and sub the wee jobs to him.

I dont think i would like to use one of these dongle types regularly but i can see the advantage of them for a very rare occasion .Just as i have a MFT for the testing of ""fixed equipment"" such as hand driers ,wall mounted heaters,etc as inferred in cop ..

72-van
 
Last edited:
Well, yes my first pat tester was a Claire. £1000 for a big box and a ton of kit. As I said in another link I do Daywork pricing, not unit pricing so I get a decent days wage for giving a completed folder containing properly filled out model sheets (V1 etc) and an introductory page advising on user checks etc, which makes a full impressive looking ring bound folder.

The last bloke I did work for paid me for my two days work, then showed me a copy of the last guys hit and run pat test results, all his kit on a single page with a single line for each unit. That guy paid me four times as much as he paid the previous tester, but was well impressed with the product that he got from me and has referred more work from his business contacts to me.

People are getting wise to the scammers and when they see someone doing the job thoroughly they realise that you get what you pay for
 

Reply to Using your multifunction tester to do PAT testing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
729
Hey guys I'm after a decent priced multifunctional tester . I know a few be knocking about on ebay. Can anyone name a couple that I could...
Replies
34
Views
2K
Hi All, My colleague and I are currently doing PAT/ISITEE Testing, and we've hit a snag with a bit of equipment - we've got 19" Racks for our...
Replies
8
Views
574
Hi all, The electrical network in my house (Antwerp, BE) is quite old and consists of two phases of about 140 volts. This gives me approximately...
Replies
0
Views
175
Hi all, Not sure if asking about rates is allowed, but I'm wondering what people's thoughts are on chargeable rates for PAT testing. Baring in...
Replies
5
Views
881

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock