Search the forum,

Discuss Using your multifunction tester to do PAT testing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

When I did the PAT course besides the visual inspection the only mandatory tests were insulation resistance and earth bond test the rest were optional. This presumably is why Kewtech state that their adapter allows the demanded mandatory tests to be performed. The only issue is that a multifunction tester will not be able to test earth bond at higher current ratings 8A 10A 20A etc but there are expensive battery operated PAT testers on the market which only test earth bond at about 200mA similar to the multifunction tester. Having said that the Kewtech adapater just appears to be a socket which allows access to the appliance plug pins with the L-N internally linked, if it is anything more intricate I would be interested to know.
 
Does anyone do it?

I can not find any reasons why not.

For simple PAt procedures.

The IEE guide to in-service inspection and testing of electrical equipment says that you need to carry out earth continuity, insulation resistance & a functional check.
The earth continuity test can be carried out at 20-200mA provided you flex the points of entry between equipment and plug during the test.

So according to the IEE yes you can use an installation tester :)
 
Has anyone got one of these ?

patadaptorw350h200.jpg


You plug it in to your MFT and it then becomes a PAT tester, Just wondered if there any good?
 

Reply to Using your multifunction tester to do PAT testing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
729
Hey guys I'm after a decent priced multifunctional tester . I know a few be knocking about on ebay. Can anyone name a couple that I could...
Replies
34
Views
2K
Hi All, My colleague and I are currently doing PAT/ISITEE Testing, and we've hit a snag with a bit of equipment - we've got 19" Racks for our...
Replies
8
Views
574
Hi all, The electrical network in my house (Antwerp, BE) is quite old and consists of two phases of about 140 volts. This gives me approximately...
Replies
0
Views
173
Hi all, Not sure if asking about rates is allowed, but I'm wondering what people's thoughts are on chargeable rates for PAT testing. Baring in...
Replies
5
Views
879

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock