The Ghost

So I have used CW1308 0.5mm² over a 25m. run (2 twisted pairs for 3+1 system). The bottom line is the door release (mag lock) does not work. Call and speech works on the handset so at least the person can be called and pick up the hand set and converse. I am 99% certain the wiring is correct and have the videx wiring diagrams which all look correct to their schemata. I am thinking there is ohms or vd problem so not enough voltage gets to release, so ok I use another twisted pair and double up. Anyone got info on vd and or ohms per m. on CW1308?
 
93ohm/km. The 0.50 is actually the conductor diameter and not the csa it is actually about 0.20mm2.
 
Last edited:
A while ago we used to do loads of Videx door entry systems. Wired the 12v mag locks in bell wire and the rest in twisted pairs. I'd say volt drop's your problem. Things may have changed, though.
 
You could prove the volt drop theory by measuring the voltage at the remote end and comparing it to the supply end. Obviously while the lock is taking current.
 

Reply to Videx door entry system...voltage drop on 0.5mm² in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi. Looking for help. My FiL has moved into a block of flats using the Bell 801 door release intercom for opening the main communal door to the...
Replies
2
Views
2K
I used to fit Bell door entry systems all the while about 20 years ago but I'm a bit rusty on them now, am I correct in saying if you use a DC...
Replies
1
Views
955
I am sending power to some 5v led lights about 50ft from the transformer. I was going to use some CAT6 direct Burial cable that I kept after a...
Replies
2
Views
1K
Hello, I am looking for a door entry system with fobs to operate a mag lock on a door. Ideally I would have a system which records of log of what...
Replies
6
Views
2K
Firstly, I hope it is ok to discuss the wiring of speakers here. TBH my ignorance in all things electrical knows no bounds, and I am guessing it...
Replies
31
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock