Discuss Visual check to determine tnc-s or tns in the Australia area at ElectriciansForums.net

R

Robo

Is it always possible to determine between tnc-s and tns by visual inspection. Tnc s is obviously combined N and E in the dno cut out and earth come from inside cutout.

If it was a tns would the earth always be clamped to the lead sheath of the cable. Thanks
 
Today i saw a dno and i could just see through the base where cable entered. I could see un sheathed swa which went inside cutout. Is ther any chance this could have been a tns. seperate core for each L and N and swa for earth??

Or is a tns earth always clamped to outside of cable armour before in enters cutout??

Or would this have been a split con Tnc - s .
 
yesterday i saw a 16mm earthing conductor to a bs951 clamped to supply sheath then a un-insulated swa to the terminalson the cutout for the connection terminal to make it TN-C-S
its a council house which has had a PIR done august last year so is this a TN-C-S or A TN-S lol or both I know the BS951 is a no no and the DNO need to sort ot as its there mess
no grommets where cables enter enclosure metal clad ccu 2 knockouts trunking with no lid shower IP4Xnot maintained , RCD tripping and wont hold in even with all loads and CBs off this is why i went round as its one of our friends and she was cooking tea was working then just tripped and that was that as it was Council and i wasnt getting paid told them to get council elecys out
they came tested and confirmed after 2 hrs it was the rcd they installed a double socket to one of the 2 ways working on the other side of the split load board which are both the up and down lighting circuits both 6A type Bs
these are all NICEIC contractors

I would go with ENGINEER as this is my opinion also he is spot on
 
Last edited:
a951f985.png
 
As widdler's diagram shows, if the property is supplied with splitcon then it is not possible to visually check unless you remove the cover of the cut-out. My old house was supplied in split con and to the untrained looked just like a TNCS supply.
 
i also had a property with what seemed to be tncs and tns. it had the earth coming from the sheath as well as the cut out so its not always possible just by a visual as to which one it is.
 
Never personally seen a cut out box like the one shown, ....we live and learn!!! I would still say however that in the majority of cases, you would be able to visually determine the earthing arrangement of the DNOs supply...

If you were ever unsure, then a Ze test would soon determine/confirm as one or the other...
 
Never personally seen a cut out box like the one shown, ....we live and learn!!! I would still say however that in the majority of cases, you would be able to visually determine the earthing arrangement of the DNOs supply...

If you were ever unsure, then a Ze test would soon determine/confirm as one or the other...
You still can visually, you just have to remove the cover (no testing required).
 
I had a 100A DP isolator fitted by british gas (unitied utilities) at my brothers so i can replace the two existing boards and tails , new digi meter
when i looked at the supply It has 2 supply cables I asked the meter guy was i TNS or TN-C-S

he said it was a TN-C-S but when i tested PEFC I got 2.5kA and PSCC 3.9kA on one board and on the other i got a higher PSCC of 4kA they are both fed from henley blocks which are in turn fed from the same supply
so if its TN-C-S then why the higher reading is it as i suspect that its because it has two supply cables not sure which is doing what
 

Reply to Visual check to determine tnc-s or tns in the Australia area at ElectriciansForums.net

Similar Threads

On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
470
Took a look at a block of flats today that has a TNC-S supply. Each flat is fed by a 2-core mineral insulated cable. The earth and neutral are...
Replies
8
Views
2K
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
277

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock