Discuss Volex cu rcd in the UK Electrical Forum area at ElectriciansForums.net

bjl

-
Reaction score
0
My mum has a Volex CU which has been nuisance tripping last few months, tried disconnecting, switching off various things but found nothing that causes it. After a while it will come back on, but it has gone now and will not switch back on feels as no tension in RCD switch. Problem is cannot find VR63 what other brand is compatible with volex?
 
basically, any 30mA RCD that has a similar current rating, and will fit. however, you're best finding the original fault if you are competent to do so and have the right test gear. if not, then get an electrician to attend.
 
as i said. any 30mA RCD with a rating of 63A or greater that will physically fit, will do the job. i've fitted BG RCDs in obsolete CUs with no trouble. only thing to watch out for is if L and N are labelelled the wrong way round. e.g with square/schneider, which have the L to the right and a cranked busbar round the N.
 
Strictly speaking you should only replace volex with volex, otherwise you may have warranty issues. But depending on the age of the RCD volex have been a part of the electrium group for many many years, the group also encompasses Wylex and Crabtree so all parts are pretty common if of the same age.

But the feeling of there being no tension in the RCD switch does not mean that it has failed, it is quite normal when an RCD is closed onto a fault.
 
Be worth testing the RCD. Out of interest if nothing else - see what it actually trips at. Daz
 
thanks for all that apparently iv just been told it switched back on now and nothing has been changed on the circuits off it. So hence im thinking its a faulty RCD it must be about 9 yrs old
 
thanks for all that apparently iv just been told it switched back on now and nothing has been changed on the circuits off it. So hence im thinking its a faulty RCD it must be about 9 yrs old

It may be a faulty RCD but I'm gobsmacked that you would come to that conclusion without any testing of circuits whatsoever. So if you fork out for a new RCD and it still trips....what's next? TESTING!!!....So test first rather than just guessing!
 
thanks for all that apparently iv just been told it switched back on now and nothing has been changed on the circuits off it. So hence im thinking its a faulty RCD it must be about 9 yrs old

That is highly unlikely if it has now closed successfully, for an RCD to fail to close you would normally expect a mechanical failure inside the unit, this wouldn't just go away on its own.
It is far more likely that there was/is a fault somewhere causing this tripping.
As mentioned elsewhere it won't take you long to test the RCD to confirm whether or not it is working
 
no i do not have the test equipment to test the RCD but have disconnected/ switched of circuits before to try locate fault
in that case you should not be replacing a RCD without being able to verify that it will work if and when necessary.
 

Reply to Volex cu rcd in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
320
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
745
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
787
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
910
A recent EICR turned up a fault: an RCD fused spur was feeding a socket and a shower pump, and neither socket or pump had continuity on the CPC...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock