elementps

Hi all,

Just wanting to clarify regarding volt drop.
Client is looking to add lighting to garden, to be supplied from 13a FCU, load on FCU will be less than 1A due to LED lighting.
The FCU will be an addition to a final ring circuit which serves dining room and lounge, protected by 32A MCB, actual load is probably no more than 13A.

Im getting myself confused with volt drop requirements, the volt drop on the final ring is within requirements for its load.

Now the volt drop for the garden lighting, is this taken as just the impedance from the FCU (13A fuse) or is it impedance of the ring plus the leg from FCU.

Let me know if i need to be more clear or specific?

Thanks in advance.

My back up plan is to feed the lighting from a dedicated circuit from a DB located at other end of the garden.
 
work out your VD on your installation from the FCU. then add to the VD of the RFC. that will give you the total VD for your modified circuit.
 
Volt drop is calculated from the origin to the furthest point of the circuit. So for you lighting circuit you will need two values the volt drop of the ring and the volt drop of the lighting spur.

For the ring you have to assume a "standard" value of 26A (osg 7.2.2) since you do not know the items that may be connected.
length of ring over 4 (double conductors in both directions) and design current of 26A allows you to calculate the volt drop with a volt drop of 0.018 V/m/A for 2.5 mm conductors.

add the colt drop for the spur and you can determine if this meets the minimum 6.9V required.
 
Thanks for clarification guys.

So if I was to run from a sub main is the total vd back to origin of supply or back to protective device at local sub main db?
 
All volt drop calcs have to be taken from the origin. If you are installing from a sub board then the volt drop of the sub main has to be included for any final circuits from the sub board.
 
Why are you worrying about VD from the house to the back yard - how long is the run ..size of a football field!
Also you may find that LED drivers normaly have a voltage rating from 110v - 240v A.C and as they normal are run from a constant current a slight voltage drop is not normaly an issue.

Also is the current FRC protected by a RCD as you will need the outside lighting to be!
 

Reply to Volt Drop in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I'm looking for a bit of advice on a volt drop query we have in our office. I'll explain the scenario and I would really appreciate any...
Replies
3
Views
647
Why is this still a thing, just done a quick calculation with the TLC volt drop calculator and if its a non lighting circuit the recommended size...
Replies
3
Views
937
Domestic property Supply number 1 6 flood lights 4x400watt= 1600 watts 250meters from board to closets corner of tennis courts Tennis court...
Replies
18
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, can someone give me some advice RE completing a small works certificate for a fused spur coming from a ring final. 1) In part 2 of the AMD2...
Replies
35
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock