So iv managed to find some time to crudely draw out the wiring.

You will have to forgive my poor knowledge on lighting circuits. For some people it's easy, for me it's always been a headache. Plus I hardly ever work on lighting wiring.

So, I think what we have here is 2 circuits with switch drops from both upstairs and downstairs lighting, via the red and black at each 2 gang 2 way.

The bit I cant fathom is, why are the colors for the intermediate red and black?

Have I missed something? Is the red and black in the 2 ways not a switch/perm feed?

20200521_100141.jpg

[automerge]1590052495[/automerge]
20200517_121812.jpg


20200517_121721.jpg


20200517_121244.jpg


some more photos.

may help
 
From your sketch, it looks like perfectly normal 'conversion' 2-way with the strappers in 3C+E, where someone has later broken into the runs of strappers and extended them to a new intermediate position using T+E. Since only L1 & L2 need to go via the intermediate (com just carries on through the break-in point as before) they used T+E not 3C+E.

I would say it's a scenario in which the capacitive leakage is likely to be quite high. Lots of cable runs with lots of PL and SL cores near each other.
 
I think your right.

If you drop one of the blue strappers out, the flashing stops but obviously you loose some functionality between switches.

So snubbers are the way forward?
 
Yes, but just to be sure that the leakage is not (at least partly) due to damaged cables, I would do some quick IR checks especially between PL and SL including between the two switch groups. My method for that would be to do a normal test L & N to E first with the switches in an 'on' permutation, then:

  • Switch one switch over to create an 'off' permutation
  • Disconnect PL and SL in both roses, earth both PL and SL in the upstairs rose and SL in the downstairs.
  • IR test the downstairs PL to earth, obviously if it shows zero resistance the switches are back in an 'on' permutation so flip one over.
  • Switch over both 2-ways leaving the intermediate as-is and test again, to ensure all strappers are tested against common.
  • Earth the downstairs PL, un-earth the upstairs PL.
  • Repeat steps 1-3 at the upstairs rose.

If you can't get to the roses you can do it all from the 2-ways by disconnecting the switch drops but leaving the strappers in L1 & L2. However, the switch drops are not then included and there is more of a risk of something getting disconnected and missed. It takes longer to describe than it will to do. Basically by earthing all conductors except one PL or SL you are testing the insulation on that relative to everything else of interest. If all results are good then crack on with snubber loads.
 
Yes, but just to be sure that the leakage is not (at least partly) due to damaged cables, I would do some quick IR checks especially between PL and SL including between the two switch groups. My method for that would be to do a normal test L & N to E first with the switches in an 'on' permutation, then:

  • Switch one switch over to create an 'off' permutation
  • Disconnect PL and SL in both roses, earth both PL and SL in the upstairs rose and SL in the downstairs.
  • IR test the downstairs PL to earth, obviously if it shows zero resistance the switches are back in an 'on' permutation so flip one over.
  • Switch over both 2-ways leaving the intermediate as-is and test again, to ensure all strappers are tested against common.
  • Earth the downstairs PL, un-earth the upstairs PL.
  • Repeat steps 1-3 at the upstairs rose.

If you can't get to the roses you can do it all from the 2-ways by disconnecting the switch drops but leaving the strappers in L1 & L2. However, the switch drops are not then included and there is more of a risk of something getting disconnected and missed. It takes longer to describe than it will to do. Basically by earthing all conductors except one PL or SL you are testing the insulation on that relative to everything else of interest. If all results are good then crack on with snubber loads.

I cant get to the Rose's. The 2d fittings only have L/N/E coming through the ceiling so I'd imagine the Rose's are in the void somewhere.

I'll order some snubbers then. Is there any specific type? Rating? Spec?
 
Just about to order snubber from cpc.

How are they connected into the circuit? Across live loop and neutral at the rose for upstairs and the same for downstairs?
 
In parallel with the lamps, at any convenient point in the circuit.
 
One per switched line, it's bleeding off the leakage from SL to N instead of it passing through the lamp(s).
 

Reply to Voltage on light circuit when off in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Just replaced a bathroom extractor fan. I didn't alter any wiring. Both old & new have live & switched live. Trouble is, once activated, the...
Replies
5
Views
361
Hi I replaced a Flash immersion timer with an apt one today and it seemed straightforward but just wondering should the light on isolation switch...
Replies
5
Views
422
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
575
Hi folks, Quick query for this still practicing regarding bill payment for a job not complete. My partner recently employed an electrician to do...
Replies
11
Views
1K
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
895

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock