Discuss Voltage on light circuit when off in the UK Electrical Forum area at ElectriciansForums.net

No, only one per SL regardless of how many lamps it serves, as they are all in parallel. The snubber can be placed anywhere - at one of the lamps, in the rose, in a JB where the SL and N are accessible - to bleed that SL down to N and therefore stop any and all lamps on that switch flashing.

Does anyone have experience of what value of capacitor is typically needed? I would expect 0.1μF to be fine, Xc is about 32kΩ at 50Hz, so even 100's of μA of leakage would only produce a few volts at the lamps.
 
One per switched line, it's bleeding off the leakage from SL to N instead of it passing through the lamp(s).
No, only one per SL regardless of how many lamps it serves, as they are all in parallel. The snubber can be placed anywhere - at one of the lamps, in the rose, in a JB where the SL and N are accessible - to bleed that SL down to N and therefore stop any and all lamps on that switch flashing.

Does anyone have experience of what value of capacitor is typically needed? I would expect 0.1μF to be fine, Xc is about 32kΩ at 50Hz, so even 100s of μA of leakage would produce a few volts at the lamps.

Does it make an difference that there are 2 circuits effected?

Should it be 1 snubber per SL and N, for each circuit?
 
Yes. Each SL is a separate, floating 'leakage collector' when it is switched off. It needs to be bled down to its own neutral.
 
Probably switch on the Neutral and not the live, quite dangerous really

Unlikely, since in post #9 they reported the switched feed to be 230V from earth with the lights on, and 79V from earth with them off.
 
Sorry I thought he tested between Line and Neutral. I was going to suggest test between Live and Earth at light when switch off.

I have seen something similar and the Second switch was off the first Switch Live and Switch Line in T&E.
 
Have a google on snubbers, there are ready made ones available that will have the values stated on them.
 
0.1μF is common, I can't see that a larger value would be needed for any reasonable amount of leakage, and the larger case would be harder to fit in a back box or wherever it's going.

BTW did you ever do any insulation tests on the switching as I recommended? It would be good to confirm that you are not simply concealing an actual fault.
 

Reply to Voltage on light circuit when off in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Just replaced a bathroom extractor fan. I didn't alter any wiring. Both old & new have live & switched live. Trouble is, once activated, the...
Replies
5
Views
360
Hi I replaced a Flash immersion timer with an apt one today and it seemed straightforward but just wondering should the light on isolation switch...
Replies
5
Views
420
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
574
Hi folks, Quick query for this still practicing regarding bill payment for a job not complete. My partner recently employed an electrician to do...
Replies
11
Views
1K
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
892

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock