Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss Voltage Operated Earth Leakage Circuit Breaker in the Periodic Inspection Reporting & Certification area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. BathSparks
    Offline

    BathSparks Regular EF Member

    Location:
    Bath
    An old fuse board with only 4 fuses 1 5amp, 1 15amp and 2 30amp fuses has a VOEL CB as the ADS for the whole board. I was adding to an outside circuit, one more light, using SWA cable and whisker boxes for a junction.

    When I came to testing, I was not sure how to test VOL CB. I have a Metrel multi-function tester and when I measured the loop impedence, the VOL CB tripped immediately. I do have a setting on the Metrel for these occasions that does not trip an RCD.
    I did a functional test and all was well.
    All other tests were fine.
    I can go back and do an RCD test, but is this compatible with the type of CB we have here. :confused5:
     
  2. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    replace it with an RCD. only solution.
     
    • Like Like x 1
  3. malcolmsanford
    Offline

    malcolmsanford Electrician's Arms

    If it is voltage operated ELCB, and it is easy to tell, the earthing conductor will go through the unit, the current operated ELCB, which is an old RCD basically will just have a LINE/NEUTRAl going to it.

    Voltage operated units, can not be tested by a MFT, as you need to induce a voltage across the coil of about 50volts and you would need an old tester for that. The IET now no longer recognize these units, and recommend change, as they were notorious for either tripping if someone looked at it sideways, or never trip at all
     
    • Like Like x 1
  4. BathSparks
    Offline

    BathSparks Regular EF Member

    Location:
    Bath
    Thanks. You are right of course but looks like I have opened up a right can-o-worms. May end up replacing more stuff agh!
     
  5. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    anyway, your outside light circuit needs RCD protection to comply with regs. so you've got no choice.
     
  6. malcolmsanford
    Offline

    malcolmsanford Electrician's Arms

    Is that because you expect the system to be a TT Tel
     
  7. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    nope. slipped up. was thinking not attached to main building , but that's notifiable, not necessarily needing RCD. DOH. excuse is that i've not had beer yet.
     
  8. ezzzekiel
    Offline

    ezzzekiel Guest

    also main bonding creates parallel paths that can cause the voelcb not to function had the same conundrum recently which went from just adding a spur to replacing voelcb, upgrading earth rod, main bonds, rewiring or making class2 all lights suffice to say the landlord decided the best option was not to fit the spur :(
     
Loading...
Similar Threads - Voltage Operated Earth Forum Date
Verifying your non contact voltage tester, the American way. Electrical Forum Sunday at 10:42 AM
Domestic 18th Ed. 715.422.107.2 Extra Low Voltage Lighting Question Electrical Wiring, Theories and Regulations Friday at 11:18 AM
Thread Status:
Not open for further replies.

Share This Page

Users found this page by searching for:

  1. voltage operated earth leakage circuit breakers ceased to be recognised in

    ,
  2. voltage oparated earth leakage cct braker

Electricians Directory Post a Domestic Job Post a Commercial Job