Discuss Voltage through earth to desk in the UK Electrical Forum area at ElectriciansForums.net

F

Fergus Macdonald

I built a metal desk with wood top. I just wired in a 500W heat lamp on the desk.

13A plug goes to a single metalclad socket via 1.5mm2 3 core cable.
Same cable then goes from socket to 1 way metalclad switch.
Same cable then goes from switch to heat lamp.

Earths are all connected to each other and to back boxes.

When I take my multimeter and measure between the socket screw and the metal desk I get about 10V. When I turn the heat lamp on it reads about 25V.

Is that normal? Is that something to be worried about? Metal desk is not earthed.

Thanks in advance.
 
Can't quite follow how you have you heat lamp working. Are you saying its on a trailing lead plugged into a socket outlet?
What is you multi meter? Even my MFT will display ghost voltages. A metal would not normally require bonding, in what contexts is it being used?
 
Hey.

They're all essentially in a line. In the back of the single socket both the incoming and outgoing cable are wired together into the screws.

The switch therefore only controls the heat lamp.

The end of the cable has a standard plug which goes into a wall socket.

Capture.png


Got a cheap Proster Multimeter from Amazon. Fairly consistent readings though - approx 9.8V every time and approx 25V every time. I checked the screw because I recently had a fault at my house where the screws were live. It's not an outbuilding or a shed, it's in an office.

Capture.PNG
 
Sounds to me like induced voltage which is creating a potential between your circuit earth and the desk (which I'm guessing has contact with the ground somehow. I'd wait for someone else to come along and confirm this though.
 
Have you an analogue meter to test that 'voltage' with? What supply do you have? Why do have a single socket and then switch between plug top & lamp?
 
Don't have an analogue meter unfortunately.

Added a socket because thought it would be handy but if this isn't the best way to wire it then will remove it.
 
If the desk metalwork is not connected to the earthed parts of the electrical fittings (which I presume are on the wood) or any other electrically connected objects, then it is floating i.e. not connected to anything. Voltage readings to floating items are meaningless as there is no circuit to measure. It's like asking the question: "What is the distance between point A?" All it tells you is that by the mere fact of a voltage being there, the desk is not earthed. But if it is supposed to be earthed, then you should be checking that with a continuity test, not voltage.
 
Good point. The desk is floating. However I don't get the same reading when I touch other metal floating things. Think it's safe to ignore?

Should the desk be earthed?
 
Should the desk be earthed?

To determine that, you would need to assess whether the metal desk is an 'exposed conductive part or extraneous conductive part'. In the former as it's not metal as forming part of a conductive part, i.e. the casing of a washing machine and in the later, unlikely to introduce a potential, the likely answer is no.

If you think of it like a metal sink, metal radiator, or metal window, non of which require bonding. Unless somehow you metal desk forms part of the installation of your lamp heater, switches etc?
 
Ok thanks. Desk is not part of the install in any way.

Sounds like it's safe to ignore the reading.

Is the socket safe wired like that? It's essentially like an extension with a spur for the lamp.
 
So you have made a sort of extension lead from a wall mounted 13A socket via a 13A plug and lead to a new socket and then a switch.
How are the new socket and switches mounted? into the desk wood?
As others have said you are measuring a known earth to a floating metal frame. The voltage is likely to be induced by nearby cables and has nowhere to go so just hangs around waiting for you to measure. The current is more important and I suspect the current would be unmeasurable. Touching the metal desk frame and earth has to be safe and won't be if the frame had a high enough voltage and current (that would have to be getting to the frame somehow)
 
Yes exactly. The back boxes are mounted onto the wood, not the metal.

Sorry, should've said. Did also try to get a current reading but couldn't get anything as you suggested.
 
If there is voltage around your structure and you are thinking of doing anything unusual on the desk it might add a bit of of frisson to the moment.
 
One simple option would be to run an earth from your socket extension built into the desk to the metal frame.
 
Interesting. I wondered about doing that before posting this but thought I better check out the voltage reading. Wouldn't be too hard to do and might mitigate an issue then no harm in doing it.
 
No No No. As said, if its not exposed conductive part or extraneous conductive part, bonding something can only make something more dangerous than it actually needs to be.
 
Hi - if you want another cheeky check - grab a 10k resistor and put it across your meter terminals, then try to measure your 10v again. :)
 
For peace of mind. The OP was troubled enough to measure and find a voltage (a minimal ghost voltage at that)
The desk has the extended socket installed so an earth is easily available. Use that and any ghost voltage will be gone and peace of mind is restored.
 

Reply to Voltage through earth to desk in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
537
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
840
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
650
I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables...
Replies
44
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock