L

leolec

Came across a supply for a 3 phase delta water pump at a friends farm the other day, the cable appeared too small at 2.5mm swa given the distance (1/4 mile) so far as I was concerned. The 25A 3 phase 30ma RCD had been fried but the cable looked to be ok. Not being a 3 phase expert I pointed my friend at the faulty component which allowed him to call the right supplier.

But it's left me thinking - do the normal volts drop rules apply to delta configs?
 
as far as im aware normal volt drop applies, and using cablemate, i just did a cable calc, guessing 12A FLC, 25A type D, 5.5kw pump with power factor .8
came in at 10mm2 because of volt drop.

Sounds undersized for me, but ofcourse will need all details for a correct answer
 
Well it must be a dammed small motor to be wired in 2.5mm over a quarter of a mile!!

Motors generally require being wired with a cable that is sized, that will not drop voltage during it's starting/run-up time, when a higher current is flowing than it's normal FLC...
 
Came across a supply for a 3 phase delta water pump at a friends farm the other day, the cable appeared too small at 2.5mm swa given the distance (1/4 mile) so far as I was concerned. The 25A 3 phase 30ma RCD had been fried but the cable looked to be ok. Not being a 3 phase expert I pointed my friend at the faulty component which allowed him to call the right supplier.

But it's left me thinking - do the normal volts drop rules apply to delta configs?

Is this a pressurisation unit as opposed to a genuine water pump?
 
Thanks very much for the responses - I didn't go into the problem in too much detail as it was well out of my comfort zone, it is a pump, the head must be over 100ft so it must be fairly powerful. I assumed the installer knew what they were doing as it's all connected to a uv filtration unit and looks the part. Granted its not giving a massive flow or a high pressure, but it took out the 3 pole RCD and the 3 pole 16A MCB. I've been reading one or two threads about harmonics but ....? Anyway the thought at the mo is to fit a non-return valve to the intake and move the pump next to the UV filter. Stands a chance as long as the system can be primed.
 
Is the pump supplied by an inverter drive?

I don't know - didn't get that far with it - what should I be looking for - I assumed delta as only L1 L2 & L3 went to the control switch, the chasis was earthed and the neutral from the rcd went to the met, would this be the same in an inverter drive?
 

Reply to Volts drop - 3 phase delta pump supply in the Electricians' Talk | All Countries area at ElectriciansForums.net

Similar Threads

I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi A good friend of mine is having a large electrical installation carried out in his garden.Hes had 3 prices from various electrical contractors...
Replies
9
Views
2K
Hi and thanks in advance, I have been asked to provide a new supply for a factory unit. They want supplies to...
Replies
17
Views
3K
I need a help from those on here with experience with 3 phase motors and VFDs. I have been asked to install the cable to supply a couple of pumps...
Replies
18
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock