Morning Chaps,
Thanks for your continued assistance. It is looking rather like the calcs will fail.
Does it matter that the building is empty and unlikely to be used for anything other than visiter centre in the summer?
What is the maximum LOR for RFC? 120 Meters is roughly worked out, lets say it would be the worst case. It is more likely to be about 100m if measured with a tape measure
If we calc 18 x 20 x 100 / 4000 = 9
Would it be acceptable to show these calcs?
ALso, should a job like this come up in the future how would I get round the VD?
Surely you wouldn't wire a RFC in 4mm? And there is nothing I could do about the LOR. It is purely down to distance from the DB
And my final question would be.... Am I correct in stating LOR as beggining at DB going to every socket and include the return leg to DB?