Discuss Wago 221 + box = replacement for 30A junction box? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
7
Hi,

I need to swap out a damaged 30A junction box on an existing ring main circuit and thought I'd replace it with Wago 221 connectors and a Wago box, but got a bit concerned by the multiple ratings on the sides of the connectors.

Can I simply swap out an old 30A JB with Wagos? Will it be sufficiently rated?

Thanks in advance!
 
There are two ratings printed on them because current ratings are defined in different ways by different authorities. The 20A rating is as per UL approval in North America, 32A as per IEC which is what we usually work to in the UK.

However, if the joint has to be maintenance free to BS5733, then the connectors are derated to 20A because the temperature rise has to be reduced to guarantee exceptionally long lifespan. That derating never occurs on a traditional 30A JB because it's not suitable for MF locations. Cables and accessories used in a 32A RFC must be rated at least 20A so the Wago 221 is still suitable whether MF or not.
 

Reply to Wago 221 + box = replacement for 30A junction box? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. I'm going to replace some sockets during a routine redecoration of our lounge including replacing some singles with doubles with USB...
Replies
2
Views
686
Hi, Have a question about wago connectors. Looking for suitable wagos for connecting 4mm twin and earth stranded (7 strands), I already have some...
Replies
2
Views
2K
I'm having a bit of a disaster at the minute and would like an honest opinion. I am having a gas stove fitted in the corner of my room and...
Replies
6
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I'm currently refitting a bedroom which has 3 double sockets and a 13 amp FCU (for a wall mounted TV). On inspection the wiring is as shown in...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock