Hi. I wanted to run a 5amp fused spur from a nearby socket but find its already a spur ( only one cable in).
Help please.
 
Now that is a coincidence
keep an eye on this thread.
 
Are you sure its a spur from a ring, and not a radial circuit direct from board? (likely 32A breaker if ring, 16A if radial)
If it is a spur from a ring, can it be modified to become a fused spur? (unswitched fuse plate next to socket on ring before the branch)

As this thread, and the other similar thread linked above, the letter of the law in the regs book says no spur from a spur, and it mentions "points" whether that be a socket, or in your case a fused connection.

Safe, but not technically compliant.
 
Are you sure its a spur from a ring, and not a radial circuit direct from board? (likely 32A breaker if ring, 16A if radial)
If it is a spur from a ring, can it be modified to become a fused spur? (unswitched fuse plate next to socket on ring before the branch)

As this thread, and the other similar thread linked above, the letter of the law in the regs book says no spur from a spur, and it mentions "points" whether that be a socket, or in your case a fused connection.

Safe, but not technically compliant.
Mm never thought it might be a radial and not at home just now to review but will have a look. Thanks for the advice. Appreciated
 
Are you sure its a spur from a ring, and not a radial circuit direct from board? (likely 32A breaker if ring, 16A if radial)
If it is a spur from a ring, can it be modified to become a fused spur? (unswitched fuse plate next to socket on ring before the branch)

As this thread, and the other similar thread linked above, the letter of the law in the regs book says no spur from a spur, and it mentions "points" whether that be a socket, or in your case a fused connection.

Safe, but not technically compliant.
Turns out this was a spur from another socket. Decided to call in a pro. He is dropping in a dedicated circuit from a spare on the consumer unit. Thanks for the swift replies.
 

Reply to Wall lights 5 amp fused spur in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
407
Hi I have a switched fuse spur where the cooker hood should plug in to… above the actual cooker. I was wondering if I could swap this out for a...
Replies
7
Views
575
I have a question which is confusing me and I cannot find a definitive answer and I hope someone can help. So I have a PC and Monitor and I have...
Replies
4
Views
439
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
672
Evening all, I’m looking to install an outside light as a spur from a socket on a ring main. There is already a spur from this socket supplying...
Replies
11
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock