OP
GreenGoblin
DIY
- Reaction score
- 2
Just done this and I can confirm I still have power to the washing machine.Try this now: Leave breaker A on, switch off B, do you have power to the w/machine?
Discuss Washing machine intermittently trips RCD. Manufacturer declares machine fault-free and suggests faulty home electrics. What should I do? in the UK Electrical Forum area at ElectriciansForums.net
Just done this and I can confirm I still have power to the washing machine.Try this now: Leave breaker A on, switch off B, do you have power to the w/machine?
If it is the 32A MCB tripping and not the one that the washing machine is on that is worrying. That sounds like a loose connection somewhere that is being shaken by the start of the cycle and shorting something outThe machine and all the kitchen appliances apart from the boiler are covered the 32A circuit breaker on the far left (labelled A). The actual breaker (also 32A) that trips when the machine is on is the one next to it (second from left, labelled B). It is responsible for
Do you mean a loose connection inside the washing machine? Or on my electrical system?If it is the 32A MCB tripping and not the one that the washing machine is on that is worrying. That sounds like a loose connection somewhere that is being shaken by the start of the cycle and shorting something out
I tried that yesterday when I was working out which circuit breaker is responsible for each set of sockets and lights. I can confirm that when I switch off A and leave B on, I have no power to the washing machine.Now this: Switch off A, switch on B, do you have power to the W/M?
Thanks - the picture definitely helps.Here is picture of my unit. Sorry about the quality - the lighting is not very good at the moment. I will try to get a better picture tomorrow during the day. The machine and all the kitchen appliances apart from the boiler are covered the 32A circuit breaker on the far left (labelled A). The actual breaker (also 32A) that trips when the machine is on is the one next to it (second from left, labelled B). It is responsible for all the devices I listed in my earlier post:
Thank you.Thanks - the picture definitely helps.
There may have been some confusion with definitions.
If the breaker B trips, even though Breaker A appears to supply the power to the washing machine then (assuming it's not just coincidental which seems unlikely) there is either a mis wiring between the circuits which needs to be fixed, or the vibration of the washing machine is disturbing a fault in the cable for the other circuit. (Or both)
Both would need diagnosing on site by an electrician with the right test equipment.
It is possible that the neutrals are not correctly split between breakers A and B. If that is the case, then circuit B could still be 'live' when breaker B is off, or vice versa with A.
Therefore until you can get it inspected, don't assume that either circuit is electrically isolated unless the RCD is off, even if the appliances plugged into it aren't working..
Leave Bosch alone. You have a problem with your electrical installation. Get an electrician.Thank you.
My kitchen work top is an L shape. The machine is located under the short side of the "L". The single dedicated mains socket for the machine is located in the corner of the L. There is wooden panel (it's part of the kitchen unit) separating the socket and the machine. Do you think the vibration of the machine could still affect the mains socket? The actual RCD box is located on the opposite side wall of the machine (away from the machine).
Should I definitely forget about going to Bosch? Can I still use the machine? I used it yesterday and it didn't trip.
I would say at least until the wiring is clarified it's not worth going to Bosch. The issue with the breakers may or may be relevant to the washing machine but needs to be sorted and they will do nothing if they can in any way pin it on the installation anyway.Thank you.
My kitchen work top is an L shape. The machine is located under the short side of the "L". The single dedicated mains socket for the machine is located in the corner of the L. There is wooden panel (it's part of the kitchen unit) separating the socket and the machine. Do you think the vibration of the machine could still affect the mains socket? The actual RCD box is located on the opposite side wall of the machine (away from the machine).
Should I definitely forget about going to Bosch? Can I still use the machine? I used it yesterday and it didn't trip.
In your wiring (or just possibly in another appliance, but very unlikely as repeatedly tripping a 32A breaker would cause a 13A fuse to fail very quickly).Do you mean a loose connection inside the washing machine? Or on my electrical system?
I really appreciate the advice. Based on what you and others have said, I'm not going to bother Bosch again. I've not done anything myself to the wiring in the 16 years I've been here. The machine sits on a solid tiled floor in the kitchen. There is some visible vibration on the machine when the starts to ramp up or slows down, but this same machine for going for two years in the same location without tripping. Perhaps it gradually slightly moved out of place over the years and this is causing problems. I just don't know.I would say at least until the wiring is clarified it's not worth going to Bosch. The issue with the breakers may or may be relevant to the washing machine but needs to be sorted and they will do nothing if they can in any way pin it on the installation anyway.
The consumer unit appears to be old but a good brand and well installed with isolator etc, so it may well be something simple. Has the wiring for the kitchen been 'upgraded' at any point by a kitchen fitter or similar? Is it a solid floor? or could there be hidden junction boxes etc below the floor or on joists that might be affected by vibration?
There may be multiple causes/faults occurring here so it is hard to give an opinion on continued use, although the RCD protection reduces the risk to some extent (assuming it continues to work correctly)
A Breaker (MCB) tripping more than once is usually a more significant fault than the intermittent RCD type fault and that should be of concern, so I would be getting an electrician to look at it sooner rather than later.
Thing is, all the sockets on circuit B are located in the hall, my bedroom and the living room (based on my investigation). The sockets in the kitchen (including the one that the machine is on) are all on circuit A, so I don't understand how circuit B's sockets could be disturbed by the vibration from the machine when none of them are located near the machine.In your wiring (or just possibly in another appliance, but very unlikely as repeatedly tripping a 32A breaker would cause a 13A fuse to fail very quickly).
My own suspicion is there is a loose wire in the back of one of the sockets on the circuit 'B' that is tripping, and it is the vibration from the machine starting a spin that is triggering the fault. So probably it is a socket (or maybe junction box) that is physically close to the machine to be disturbed.
But as already said above, it really needs an electrician to visit and check things out!
I really appreciate the advice. Based on what you and others have said, I'm not going to bother Bosch again. I've not done anything myself to the wiring in the 16 years I've been here. The machine sits on a solid tiled floor in the kitchen. There is some visible vibration on the machine when the starts to ramp up or slows down, but this same machine for going for two years in the same location without tripping. Perhaps it gradually slightly moved out of place over the years and this is causing problems. I just don't know.
I plan to book the electrician in for Thursday, but I desperately need to use the machine tomorrow. I was just hoping it would be okay to use for one more wash before the electrician looks at it. It's pretty clear I need to get it looked at. I don't know anyone else that I could ask for advice, so I am really grateful for the advice from you and others in this thread.
Do you know if the cables might run through/past the kitchen area (based on where the CU is located)?Thing is, all the sockets on circuit B are located in the hall, my bedroom and the living room (based on my investigation). The sockets in the kitchen (including the one that the machine is on) are all on circuit A, so I don't understand how circuit B's sockets could be disturbed by the vibration from the machine when none of them are located near the machine.
Thanks. I'd be running a full wash cycle so spins would be unavoidable. I will give it some thought overnight and see whether it's worth taking the risk. On the positive side, at least I now know the next step I need to take in regard to solving the problem.It sounds like it may be the vibration that causes the issue, so is it possible to use the machine on a cycle without the spin?
Obviously noone can guarantee that using it once more wouldn't cause a further problem. However, turning breaker B off before you run the washing machine would seem to minimise the risk of the fault occuring on that circut, especially if it is vibration causing the problem, and not interlinked wiring (though it may still trip the RCD).
Thing is, all the sockets on circuit B are located in the hall, my bedroom and the living room (based on my investigation). The sockets in the kitchen (including the one that the machine is on) are all on circuit A, so I don't understand how circuit B's sockets could be disturbed by the vibration from the machine when none of them are located near the machine.
But as you say, it's best to get the electrician in. Thanks for your thoughts.
The CU is located in the kitchen on the opposite wall of the machine. If you could imagine an L shape worktop, the machine is under the short side of the L and the CU is on the opposite wall (imagine another short line at the top of the L). My home is an ex-council 2-bed flat so it's a very small kitchen. There's wiring in a slim plastic sheath running across the walls into the CU, but from what I can see, it's well away from the machine.Do you know if the cables might run through/past the kitchen area (based on where the CU is located)?
Also there is rarely much vibration is houses to match a washing machine starting spin, so even though it is a few meters away it might just be enough to case the problem.
As above, it is probably OK to use the machine tomorrow but I would not run it unsupervised just in case.
Hopefully you can let us know what is found & fixed?