When carrying out a PIR do you actually have to see the earth clamp on the water pipe?
I've had a few jobs lately where only the stopcock can be seen at the back of the kitchen cupboard and everything else is boxed in. I check continuity from the stopcock back to the CU and that is ok, but do I actually have to physically see the clamp? I know the regs say that bonding has to be within 600mm but this will mean pulling the kitchen cupboard to bits.
 
the clamp should be accessible for inspection. i'd give it a code 4 at least, maybe even a code 2.
 
As the others state....not visible will get a code.
The problem with relying on a continuity test is that with parallell paths you may get a perfectly good reading even if the bonding is not present.
 
i don't give it a code provided the continuity test is less than the stated maximum of 0.05 ohms (as per guidence note 3, 612.2.1) and make a note on the paperwork that the connection was not visible or accessible
 
Not sure what you mean by a potential difference test, if you are referring to a continuity test then, as stated above, parallel paths through other bonding and by misidentification of the bonding conductor may invalidate the result but in general if there is a low resistance to the water it is bonded but maybe not according to the regulations.
 
hi what i meant was if you used a voltage tester and placed one probe onto a live and the other onto the water pipe if you get a pd of 230 volts doesnt that mean the pipe has a pathway to earth
thanks for your reply
 
hi what i meant was if you used a voltage tester and placed one probe onto a live and the other onto the water pipe if you get a pd of 230 volts doesnt that mean the pipe has a pathway to earth
thanks for your reply

You are missing the point of bonding....incoming services need to be bonded because they already have a path to earth,not because they dont....this is why tests are unreliable as a means of confirming bonding,and why it needs to be visible for inspection.

Incoming services may introduce an external earth potential into the building.During fault conditions conductive parts within the building may be subject to a rise in potential relative to the general mass of earth untill the protective device clears the fault. Anyone in contact with a conductive part under these conditions may be at risk of a shock,in practice that person is likely to be insulated from the general mass of earth by virtue of being stood on an insulating floor..(wood,dry concrete etc)...so the risk is minimal.
However incoming metallic services effectively introduce the general mass of earth into the building,now anyone in contact with a conductive part at the same time as an extraneous conductive part during the fault will receive a serious shock....by tying conductive and extraneous parts together by bonding there can be no potential difference between them and a reduced shock risk.
Remove from your grey matter the notion that bonding is earthing the pipes,it is an entirely different thing.
 
Last edited by a moderator:
many thanks for your reply you have pointed out to me something i knew but but hadnt thought of i over looked the obvious
your info has given me a greater insight and more working knowledge
 

Reply to Water bonding on a PIR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
evening everyone . Quick question here I’ve recently took over a job that a friend of mine first fixed it’s a 3 bed semi house rewire. I don’t...
Replies
10
Views
1K
Disclaimer: I'm not going to attempt this job myself, I want a professional to do this job properly since I consider it non-trivial and need it...
Replies
2
Views
900
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
462

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock