Hi,

I have to bond the water and gas on a TT installation, the electrode has a 10mm/sq to it already. Its my mate`s house and I`m adding a new lighting circuit for my DI assessment. My mate has got some 16mm/sq G & Y lying around. Can I use this to bond the gas & water while the main protective conductor remains at 10mm/sq?

Thanks
 
I *believe* I'm right in saying that the conductors on a TT system only have to be 4mm max if they're not buried so you can do what you like above that.
 
with the price of 16mm, i'd save it for main earthing on other jobs and buy some 6mm for this one.
 
the CSA of the earthing conductor in TT installations is governed by the Ra of the rod. the lower the resistance, the higher the fault current, and the larger the cable needs to be as a result.
 
I'll hold my hands up to knowing little about TT requirements (through necessity) and even after having a look through the OSG I can't find 6mm mentioned. Could you point me in the right direction please? :)

Minimum CSA for earthing conductors, is 2.5mm² (if sheathed).
Minimum CSA for bonding conductors, is 6mm².
 
I did a Ze test a while back on this one and got a reading of about 150 ohms which to me is ok ( under the 200 ohm mark ). It was the 16mm gas and water I was wondering about.
How does that sound mate?
 
I'll hold my hands up to knowing little about TT requirements (through necessity) and even after having a look through the OSG I can't find 6mm mentioned. Could you point me in the right direction please? :)
"544.1.1 Except where PME conditions apply, a main protective bonding conductor shall have a cross-sectional area not less than half the cross-sectional area required for the earthing conductor of the installation and not less than 6mm²."
The 2.5mm² is mentioned in Table 54.1 and Regulation 543.1.1.
 
I did a Ze test a while back on this one and got a reading of about 150 ohms which to me is ok ( under the 200 ohm mark ). It was the 16mm gas and water I was wondering about.
How does that sound mate?

personally 150 ohms would be the limit, yes its fine but anything higher i would defo consider extending or adding another spike.
 

Reply to Water & Gas 16mm/sq in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
3K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
522
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
1K
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top