Hi all can someone give me some advice on what kw heater I can use with this speck
Fuse board b32 rcd
Cable 2.5.....10 metres long just for water heater (nothing else conected)
Water heater will be in downstairs clockroom and use just for hand washing.
What size in kw can I use and how can I connect
Thanks in anticipation........Keith
 
Hi thanks for your reply I had a new consumer unit fitted and the electrician was informed that it was going to be used for a small water heater.
A standard 2.5mm2 Radial would be on a 20 Amp OCPD
 
and it all depends on the installation method of the 2.5mm. if method C, then it's good for 6kW max. if in insulation, 3kW max. but that's pushing it to the limit, so I'd be inclined to downsize those figures to 5kW and 2.5kW respectively. as Rob said, the 32A MCB is OK as it's a fixed load.having said that, a site visit is needed to confirm.
 
and it all depends on the installation method of the 2.5mm. if method C, then it's good for 6kW max. if in insulation, 3kW max. but that's pushing it to the limit, so I'd be inclined to downsize those figures to 5kW and 2.5kW respectively. as Rob said, the 32A MCB is OK as it's a fixed load.having said that, a site visit is needed to confirm.
Hi telectrix thanks for your reply ......the cable runs under kitchen cabs up though a stud wall without insulation into a loft space above the insulation,so if I read your info correctly it will be ok with 3.5 to 4 kw ?
 
Best you get the circuit checked.

New circuits, like fuseboard changes fall under part P of the building regs
As i read it, the circuit had already been installed by a spark, but without a water heater on the end of it. OP wants to fit one and is asking for advice on what size he can get. even so, i's get a local sparks to check the circuit and advise accordingly.
 

Reply to Water heater wiring advise please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
221
Evening Gents just after a bit of advice and what would you do differently. I have wired up 3 kw heaters in 4mm tuff cable (40 meter distance...
Replies
2
Views
256
Can anybody advise? I have a 3 rate old style electricy meter with 3 rates (day, night, and stored energy) Storage heaters are completely off at...
Replies
1
Views
760
Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock