Could be the parallel path causing the trip.
From what's been said, I think this is the most likely reason.
I'm suspecting a N-E fault to something that isn't the CPC of that circuit.

I'd repeat IR tests with all parallel paths connected. I know you tested low resistance to the pipe near it but it might be something else.
You could also try running a temporary N conductor from switch to light, using original switched live.

Ultimately though you've proved it's that particular cable upsetting things somehow, and unless it's easy to run another one I'd start focussing on a solution that doesn't involve it, as it's probably unlikely you'll be able to repair whatever the issue is very easily.
 
How old is this property? Does the RCD trip with a loud 'pop', or does it just click off? Is there any delay at all, or does it trip immediately on energising?

3 possible faults that I can think of:

1 - Regular earth fault, but perhaps you're doing something not quite right with your testing, so it's not showing up.

2 - Borrowed neutral/interconnected circuits. This won't necessarily show as low IR to earth.

3 - Fault between L and E that is not quite touching, but arcs intermittently. I have come across this only once. It gave no indication whatsoever on an IR test at 500V, but would intermittently trip the RCD (and sometimes MCB) with a loud 'pop'. Traced to a nicked live conductor that was arcing to the backbox.

Here's what I'd do:

Main switch off. Put everything back together, as it was. Lamps must be in place, nothing disconnected/bypassed. All light switches etc in the 'on' position.
Disconnect the suspect circuit L+N conductors from the MCB and N bar, and join together. Leave CPC in earth bar.

At 250V, IR test between the faulty circuit and E bar, then N bars, then each and every MCB outgoing L terminal. If all results are reasonable, try again at 500V. If you're still getting reasonable results, then 1 and 2 are eliminated, and it has to be 3.

Good luck!
 
How old is this property? Does the RCD trip with a loud 'pop', or does it just click off? Is there any delay at all, or does it trip immediately on energising?

3 possible faults that I can think of:

1 - Regular earth fault, but perhaps you're doing something not quite right with your testing, so it's not showing up.

2 - Borrowed neutral/interconnected circuits. This won't necessarily show as low IR to earth.

3 - Fault between L and E that is not quite touching, but arcs intermittently. I have come across this only once. It gave no indication whatsoever on an IR test at 500V, but would intermittently trip the RCD (and sometimes MCB) with a loud 'pop'. Traced to a nicked live conductor that was arcing to the backbox.

Here's what I'd do:

Main switch off. Put everything back together, as it was. Lamps must be in place, nothing disconnected/bypassed. All light switches etc in the 'on' position.
Disconnect the suspect circuit L+N conductors from the MCB and N bar, and join together. Leave CPC in earth bar.

At 250V, IR test between the faulty circuit and E bar, then N bars, then each and every MCB outgoing L terminal. If all results are reasonable, try again at 500V. If you're still getting reasonable results, then 1 and 2 are eliminated, and it has to be 3.

Good luck!

Thanks for the tips. Will give them a try.

To answer your questions.

Property is 12 years old and RCD clicks off immediately on energising. Ie I can’t even energise it as it trips straight away if the light is in the on position. If it’s off then it will energise but immediate trip when the light is turned on.

I don’t think I’m doing anything wrong with my testing and when I rang tech support and talked through exactly what I’d done they didn’t say I’d done anything wrong.

I don’t think there are any borrowed neutrals. Certainly not at any of the switches and I’ve had most of the light fittings down.

A lot of the back boxes have a lot of cables in due to the loop being at the switches. But I had all the switches off and the common was linked through with Wago’s to take out all the other lights in the circuit. So I can only think I that scenario there is rodent damage that is arcing once the circuit tries to energise.

I’ll do the 3 steps you mentioned and see how it goes. Thank you. I do appreciate the advice as I’m far from a font of all knowledge and always happy to learn. 😊
 
When IR testing are you sure the CPC is linked back to the MET?

If you have narrowed it down to a length of cable are you sure it has no junction box to some other thing?
Yes it’s linked as R1+R2 tests fine.

I’d be surprised if the cable has a junction box as it goes down the wall from the switch, underfloor across landing and up the wall to the light. But as it’s buried in the walls I will only be able to check the underfloor section unless the owner decides to have to pulled out and new cable chased in.
 
I have had similar type of faults and they all have turned out to be faulty cable shorting out under mains power.Your test meter cannot supply enough power to leap the faulty area but mains power certainly can.Sometimes 1000v on the tester might just about show it up but still no guarantees.
Mains power has much more potential to jump gaps than your tester can.
 
I have had similar type of faults and they all have turned out to be faulty cable shorting out under mains power.Your test meter cannot supply enough power to leap the faulty area but mains power certainly can.Sometimes 1000v on the tester might just about show it up but still no guarantees.
Mains power has much more potential to jump gaps than your tester can.
Fully agree.The OP is basically describing what is a "high resistance" fault for a test meter but that becomes a "low resistance" fault once mains power is applied.Typical of water faults and other foreign matter
 
Mains power has much more potential to jump gaps than your tester can.

It's not power that decides how far a spark will jump or how insulation will break down, it's voltage, With the peak voltage of 230V mains being 325V, a 500V insulation test will create more stress and a 1000V test much more stress and is more likely to cause it to break down to an extent that shows as a bad reading. The power behind the mains is likely to do vastly more damage and create a much more noticeable effect if it breaks down catastrophically, but a 230V RMS sinusoid won't jump as big a gap in the first place.

When we get into the realm of fast-risetime pulses, things get a bit more complex as dv/dt is important as well as voltage itself, but not applicable to normal mains or DC insulation testers. A 4kV surge on the mains could show a lot of things up but again that's out of the realm of the comparison being made.

As far as the circuit fault is concerned, I agree that a short between this circuit and another is a likely culprit. When testing for an elusive fault like this, far from separating the CPCs etc my first move would be to link everything together that can be linked, all L's, N's, CPCs, other than the conductor under test. Anything to prove that the insulation of that one conductor is breached, before splitting it down again to localise.
 

Reply to Weird fault that no-one can work out the issue. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
1K
I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
361
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
377
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock