Discuss weird lighting fault in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
56
Hi folks
while testing this theatre, i attempted to get a Zs from an emergency exit sign. The steel conduit is being used as cpc.
when i connect my three probes to l,n,earth i'm getting 110v on the screen and when i press test it comes up with about 160 ohms.
i put a voltmeter across and found 110v between L and E but 230v between L and N.
could this be a poor connection on the steel conduit cpc and if so, why does the voltage drop to approx 110v

thanks...its a bit of a puzzle
 
do a R2 test on the conduit end to end. then test to MET.
 
even if it's 3000m you've got to get it right, one way or another. do it in stages with a wander lead.
 
code 1 it and FIX it. you don't put a band- aid on an arterial bleed.
 
probably getting a reading through the damp walls, and forgot to mention, you should not walk away from a code 1, without isolating or rectifying.
 
only 76, must have been done on a good day.
 
I assume you are doing a PIR ?
Conduit as CPC 35 years old
76 code 1's so far I guess the recommendation is a full re-wire
As for 110V L-E try testing much closer to the main DB
I guess the conduit is badly corroded at various points and is a very high resistance compared to L-N insulated copper conductors
 
assuming it is a bad earth, can someone please explain the science behind it...how does it become 110v???
If you've got good Zs figures elsewhere you can rule out the earthing conductor itself.
So if we're dealing with a fault on just this one conduit run, here goes:

Let's assume:
The conduit is completely open circuit quite near the origin.
The insulation resistance L-E is 0.5Meg and N-E is 0.5 Meg. (measured at end of circuit)
Voltmeter input impedance is 10Meg.

Think of a potential divider, L to N, with the conduit in the middle
For a 230V supply, you'd get a theoretical 115V
But with the 10 Meg of your voltmeter in parallel with whichever 0.5Meg you were measuring across, the voltage seen would reduce slightly.

Now if you've got a measured Zs of 160 Ohm and 110V L-E, sounds like something is corroded AND full of water

Unless someone's made up an IT system, centre tap earthed through an impedance....

Simon.
 

Reply to weird lighting fault in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
676
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
764
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
658
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
473

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock