Does this sound like a normal way of wiring a PIR.
So had to change a PIR for a pullcord today and this caught me out. Just wonder what others thoughts are.
I could not get to any of the wiring above at all. I had two Twin and earth cables coming to PIR.
1st cable was power in no problem.
2nd cable, the line and cpc buzzed out to the first downlight (took all downlights apart to make sure I could work out where the cables were going but they were all just normal daisy chained together). However Neutral there was nothing to the downlight. You could pull the cable so so was clearly the same cable but could have had a junction box connected to it that was moving with the cable.
When you turn power on the cables at the PIR, the 1st cable was normal as expected, 2nd cable was 230v on the neutral conductor.
I ended up just having to wago up the second cable at the PIR and light and run a new cable wiring a light switch like you would normally with power going to the switch.
There did not appear to be another switch anywhere and the client didnt know of any other switch, thats the only thing I can think of that there was another source of power to a switch which was providing Neutral to the first light and then the permanent live to the PIR switch via the neutral then the SL going to the light from the other side of the PIR switch. I guess you could then turn the lights off of using the switch (although power would still be at PIR), it obviously was not an overide to turn on as there was 230v on the neutral so the lights would have been on all the time.
Apparently the previous owner was a "Sparky" and had offered to change the PIR for a pullcord as it was an easy job so client maybe thought it was me. Ended up there basically all day and after parts etc probably made about a tenner for a days work as kept to my quote.
I am guessing its been messed around with and maybe the switch was changed to a junction box somewhere as was decided was not needed as could not see any other switch for the life of me anywhere.
Am I missing something or does that wiring sound really strange? Sorry just bit miffed for working all day for bugger all (I need to get harder but the client was a skinflint and its a small town where reputation is everything).
So had to change a PIR for a pullcord today and this caught me out. Just wonder what others thoughts are.
I could not get to any of the wiring above at all. I had two Twin and earth cables coming to PIR.
1st cable was power in no problem.
2nd cable, the line and cpc buzzed out to the first downlight (took all downlights apart to make sure I could work out where the cables were going but they were all just normal daisy chained together). However Neutral there was nothing to the downlight. You could pull the cable so so was clearly the same cable but could have had a junction box connected to it that was moving with the cable.
When you turn power on the cables at the PIR, the 1st cable was normal as expected, 2nd cable was 230v on the neutral conductor.
I ended up just having to wago up the second cable at the PIR and light and run a new cable wiring a light switch like you would normally with power going to the switch.
There did not appear to be another switch anywhere and the client didnt know of any other switch, thats the only thing I can think of that there was another source of power to a switch which was providing Neutral to the first light and then the permanent live to the PIR switch via the neutral then the SL going to the light from the other side of the PIR switch. I guess you could then turn the lights off of using the switch (although power would still be at PIR), it obviously was not an overide to turn on as there was 230v on the neutral so the lights would have been on all the time.
Apparently the previous owner was a "Sparky" and had offered to change the PIR for a pullcord as it was an easy job so client maybe thought it was me. Ended up there basically all day and after parts etc probably made about a tenner for a days work as kept to my quote.
I am guessing its been messed around with and maybe the switch was changed to a junction box somewhere as was decided was not needed as could not see any other switch for the life of me anywhere.
Am I missing something or does that wiring sound really strange? Sorry just bit miffed for working all day for bugger all (I need to get harder but the client was a skinflint and its a small town where reputation is everything).