During the no-load test of a transformer, the primary winding is connected to an AC source without any load connected to the secondary winding. In this condition, the transformer draws only magnetizing current which is required to magnetize the core and establish a magnetic field in the transformer. The unbalance current during the no-load test of a transformer may be caused by several factors including:

  1. Magnetic imbalance: If the transformer core is not symmetrically designed, or if there is any damage or manufacturing defect, it may cause magnetic imbalance which will result in unbalanced current during no-load operation.
  2. Open circuit: If there is an open circuit in the winding of the transformer, it may cause an unbalanced current during no-load operation.
  3. Insulation failure: If there is an insulation failure in the transformer winding, it may cause a current imbalance during no-load operation.
  4. Voltage imbalance: If there is any voltage imbalance in the power supply, it may cause current imbalance during no-load operation.
  5. Unbalanced core magnetization: If the transformer core is not uniformly magnetized, it may cause an unbalanced current during no-load operation.
To determine the exact cause of the unbalanced current during no-load operation, a detailed analysis and testing of the transformer is required. It is important to identify and correct the cause of the unbalanced current to prevent any damage to the transformer and to ensure its proper operation.
 
How big is the imbalance? Have you got the no-load current values? The incoming voltages?

Also when / how did you notice there was a problem?

If it really is recent then it is unlikely to be the core (unless someone applied a LOT of force, or an earthquake) and that would suggest insulation failure as most likely to me. But I don't know as much on this as the likes of @Julie. or @plugsandsparks
 
How big is the imbalance? Have you got the no-load current values? The incoming voltages?

Also when / how did you notice there was a problem?

If it really is recent then it is unlikely to be the core (unless someone applied a LOT of force, or an earthquake) and that would suggest insulation failure as most likely to me. But I don't know as much on this as the likes of @Julie.

How big is the imbalance? Have you got the no-load current values? The incoming voltages?

Also when / how did you notice there was a problem?

If it really is recent then it is unlikely to be the core (unless someone applied a LOT of force, or an earthquake) and that would suggest insulation failure as most likely to me. But I don't know as much on this as the likes of @Julie. or @plugsandsparks

How big is the imbalance? Have you got the no-load current values? The incoming voltages?

Also when / how did you notice there was a problem?

If it really is recent then it is unlikely to be the core (unless someone applied a LOT of force, or an earthquake) and that would suggest insulation failure as most likely to me. But I don't know as much on this as the likes of @Julie. or @plugsandsparks
TR rating: 5KVA, Step up: 0.470KV / 22KV, No Load current: 8Amp, 0.14Amp, 7.8Amp, Primary side applied Voltage: 0.4KV, Transformer service is as HV power supply unit including rectifier circuit.
 
TR rating: 5KVA, Step up: 0.470KV / 22KV, No Load current: 8Amp, 0.14Amp, 7.8Amp, Primary side applied Voltage: 0.4KV, Transformer service is as HV power supply unit including rectifier circuit.
Primay side winding resistance: 629m-Ohm, 643m-Ohm, 631m-Ohm
 
TR rating: 5KVA, Step up: 0.470KV / 22KV, No Load current: 8Amp, 0.14Amp, 7.8Amp, Primary side applied Voltage: 0.4KV, Transformer service is as HV power supply unit including rectifier circuit.
Primay side winding resistance: 629m-Ohm, 643m-Ohm, 631m-Ohm
What is the winding group?

Yny Or Ynd1?
 
I can see why you are querying these numbers. When you say there is a rectifier on the output is this rectifier connected when you are seeing these numbers? - Has the rectifier been tested to ensure all stages are working ?
 
I can see why you are querying these numbers. When you say there is a rectifier on the output is this rectifier connected when you are seeing these numbers? - Has the rectifier been tested to ensure all stages are working ?
No, Rectifier is not connected, Primary is delta connected at 400V and Secondary is star connected at 22,800V.
 
Have you got access to each set of windings separately at some connector board?

I.e. can you separate the delta and energise each of the 3 separately to test each on a single phase supply?
 
dY11 and Primary is delta connected at 400V and Secondary is star connected at 22,800V.
OK

Since you see the current between two phases on the delta winding, this means the one winding is either at fault, or (more likely) the secondary has a fault - I would guess one high voltage winding has a fault somewhere along its winding to earth (the star point being earthed) or has an inter-turn winding fault.

This phase will be the one corresponding to the branch of the delta connecting both current taking phases (~8A).

Can you flash test the hv windings - ~27-35kV as it may be an insulation breakdown issue, so won't be shown via an insulation resistance test?

If its an inter-turn winding fault it is a little more difficult to detect with an assembled tx.

(The above assumes there is absolutely nothing connected on the hv side - obviously if there is a single phase load/fault in that part of the system it will reflect as a phase-phase load/fault on the primary )
 
OK

Since you see the current between two phases on the delta winding, this means the one winding is either at fault, or (more likely) the secondary has a fault - I would guess one high voltage winding has a fault somewhere along its winding to earth (the star point being earthed) or has an inter-turn winding fault.

This phase will be the one corresponding to the branch of the delta connecting both current taking phases (~8A).

Can you flash test the hv windings - ~27-35kV as it may be an insulation breakdown issue, so won't be shown via an insulation resistance test?

If its an inter-turn winding fault it is a little more difficult to detect with an assembled tx.

(The above assumes there is absolutely nothing connected on the hv side - obviously if there is a single phase load/fault in that part of the system it will reflect as a phase-phase load/fault on the primary )
The star point is not earthed, All the transformer test results are satisfactory, Test we conducted are following;
IR (Both Windings), TTR, Open Circuit Test, Winding resistance
 

Reply to What are the causes of unbalance current during no load test of transformer? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi folks I've just identified as cause of lighting circuit tripping in consumer unit a low volts ceiling light with laride transformer taking in...
Replies
7
Views
292
What are smallest in physical size split core current transformers. Max load 100amp max cable core size 35mm. Power cannot be isolated and space...
Replies
0
Views
552
I have a bathroom fan with a moisture detector that turns it on and off. It also has a control circuit to turn it on/off when moisture is not...
Replies
1
Views
333
Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
Replies
25
Views
2K
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock