Discuss what csa and material to enter in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

S

sams

Evening all,
I wonder if anybody could help me what to enter as the material and size of earthing conductor when 25mm steal conduit is used as earthing, so what is 25mm steal conduit equivalent to earthing conductor mm!
I am struggling to find out what to put down in cert.
Thank You in advace for your input
 
Hi sams, 25mm Steel Conduit has the following CSA:
Light Gauge = 89mm[SUP]2[/SUP]
Heavy Gauge = 132mm[SUP]2[/SUP]
The minimum size of CPC when the line conductors are copper and the CPC is steel:
<16mm[SUP]2[/SUP] 70°C thermoplastic line conductors require a steel CPC of =>2.45 x line conductor CSA
<16mm[SUP]2[/SUP] 90°C thermoplastic line conductors require a steel CPC of =>2.27 x line conductor CSA
So either light or heavy gauge 25mm steel conduit easily complies with BS7671 543.1 as a CPC for PVC line conductors <16mm[SUP]2[/SUP].
On your TSR you should record the CPC as Steel and it's CSA, either 89mm[SUP]2[/SUP] or 132mm[SUP]2[/SUP] as appropriate.
 
Last edited by a moderator:
Thank you very much Mark and yes this info should be in one of the sticky threds as it is very useful for other users
 
I wonder what 3” steam pipe works out at?

Don’t laugh, I tried to use it with silicon-braided singles running through it. It didn’t last long, a 70-ton cane hit it!
Back to the drawing board
View attachment 9078
 
Last edited by a moderator:
Unable to edit the #2 post, so I have re-jigged and expanded the information here.
Cross-sectional area of BS EN 61386:2004, BS EN 50086:1994 and BS 4568:1970 steel conduit.

The CSA of 16mm steel Conduit:

Light Gauge = 47mm[SUP]2 [/SUP]
Heavy Gauge = 75mm[SUP]2[/SUP]
The CSA of 20mm Steel Conduit:

Light Gauge = 59mm[SUP]2 [/SUP]
Heavy Gauge = 107mm[SUP]2[/SUP]
The CSA of 25mm Steel Conduit:
Light Gauge = 89mm[SUP]2
[/SUP]Heavy Gauge = 132mm[SUP]2[/SUP]
The CSA of 32mm Steel Conduit:

Light Gauge = 116mm[SUP]2
[/SUP]Heavy Gauge = 167mm[SUP]2[/SUP]
The CSA of 38mm Steel Conduit:

Light Gauge = Unavailable
Heavy Gauge = 186mm[SUP]2 [/SUP]
The minimum size of CPC when the line conductors are copper and the CPC is steel:
<16mm[SUP]2[/SUP] 70°C thermoplastic PVC line conductors require a steel CPC of >=2.45 x line conductor CSA (16mm[SUP]2 [/SUP]PVC =>39.2mm[SUP]2[/SUP] minimum required)
<16mm[SUP]2[/SUP] 90°C thermoplastic PVC line conductors require a steel CPC of>=2.27 x line conductor CSA (16mm[SUP]2 [/SUP]PVC =>36.32mm[SUP]2[/SUP] minimum required)
<16mm[SUP]2[/SUP] 85°C rubber line conductors require a steel CPC of >=2.48 x line conductor CSA (16mm[SUP]2[/SUP] rubber =>39.68mm[SUP]2[/SUP] minimum required)
<16mm[SUP]2[/SUP] 90°C thermosetting XLPE line conductors require a steel CPC of >=2.47 x line conductor CSA (16mm[SUP]2[/SUP] XLPE =>39.52mm[SUP]2[/SUP] minimum required)
Therefore all the above steel conduit sizes/gauges easily comply with BS7671 543.1 as a CPC for the above types and sizes of line conductor.
 
Last edited by a moderator:
Doing a conditions report on a old property and conduit used as cpc as was in the 60s.
Interesting i would like to understand were we get these figures from as the conduit there is 3/4" and 1"
Its a amazing place to test we have conversation charts as all MI are imperial so have to put down csa of coductors in mm2.
Could do with a spreadsheet to show all conduits and trunks cpc as well as old single wiring sizes as have to measue outside diameter to obtain ruff size anyone know of such a spreadsheet.
 
for the cpc csa i would just enter "conduit". let some bugger else do the calcs if they are ----.
 
Doing a conditions report on a old property and conduit used as cpc as was in the 60s.
Interesting i would like to understand were we get these figures from as the conduit there is 3/4" and 1"
Its a amazing place to test we have conversation charts as all MI are imperial so have to put down csa of coductors in mm2.
Could do with a spreadsheet to show all conduits and trunks cpc as well as old single wiring sizes as have to measue outside diameter to obtain ruff size anyone know of such a spreadsheet.
Guidance Note 8 contains information regarding Steel conduit/tray/trunking equivalence, if I'm recalling correctly.
 

Reply to what csa and material to enter in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
833
Looking for a bit of advice from the wider audience / those who may have done similar before. I entered the game a bit later / in a non...
Replies
12
Views
647
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Replies
15
Views
880

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock