Discuss what do these 380v wiring colours mean, I want to use with a 220v vfd. it may have had speed control in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
22
3-phase-wiring-question.png

Hello, I am a woodworker who has got a large old power feed, its 380v and i want someone to rewire to a 220v vfd for me, can someone please tell me what these old colour codes mean. I bought the machine in Scotland.I can't find any easy diagrams online.I think its a good few years old.Thank you!

1 2 3 4 5 6 7
 
Most likely you have a star delta wired motor. The 6 wires plus green/yellow (earth) are the ends of 3 separate windings.

It is a little to complex to explain on a forum but it is unlikley to be possible to use a single phase vsd, you will probably need a 3 phase one or a new motor.

To confirm, can you post a pic of the motor rating plate?
 
Most likely you have a star delta wired motor. The 6 wires plus green/yellow (earth) are the ends of 3 separate windings.

It is a little to complex to explain on a forum but it is unlikley to be possible to use a single phase vsd, you will probably need a 3 phase one or a new motor.

To confirm, can you post a pic of the motor rating plate?

Thank you, i will do that tommorow.
 
No you cannot just rewire a three phase motor so it will run on a single phase supply,
you can how ever get a electronic convertor / motor speed control
not cheap mind you but will work splendidly
 
Most likely you have a star delta wired motor. The 6 wires plus green/yellow (earth) are the ends of 3 separate windings.

It is a little to complex to explain on a forum but it is unlikley to be possible to use a single phase vsd, you will probably need a 3 phase one or a new motor.

To confirm, can you post a pic of the motor rating plate?
79323948_2394291114215533_5123692591656730624_n.jpg
79433539_1195855287284895_7711502475890524160_n.jpg
79680116_561356141317943_5203009784231493632_n.jpg


Thank you, I think i see what you mean about complicated.
View: https://www.youtube.com/watch?v=h89TTwlNnpY


I will have to work out what motor to replace it with, guessing if it is a stardelta motor arrangement this would have to have a separate panel with switches and timers? and 3 phase., this is likely too expensive for me to setup. I need to figure out an alternative to closely match performance, if you could let me know what I should look for off the name plate, that would be amazing.

Iv tried to take good pics, its very shiny and hard to read.

The two pics are of the left and right sides of the plate.

If you're not able to read it, please let me know and I will write it out.

Thanks a million.
 
Ok, it’s got 6 windings inside, wires star, star.
An unusual setup for such a small motor.
Y is the symbol for star and the triangle is the symbol for delta.

It is probably cheaper to replace the motor with a single phase motor.
Unless you need variable speed.
In that case I would go for a 3ph 230v motor and a vfd

I can’t see any numbers after the triangle n the voltage area of the plate.
[automerge]1576428183[/automerge]
Something like this might do you well
You will have to check dimensions and shaft size etc

 
Last edited:
Thank you very much.

These numbers read off the plate.

380yy delta

0.25kw

1370/80 rpm? I can detach from the gearbox

0,75/0,75 A
Co's 84/.62

Ip44

Have read these straight off

I'm new to motors, 3ph 3 phase 240 v motor

What horsepower or or kw.

How do I know the torque required?

It powers 9 wheels via sprockets and chains. It needs to be strong.

I might have to get a custom mounting plate made.

It's worth getting it working but is there a way I can get a suitable 240v motor at variable speed and suitable torque?






Ok, it’s got 6 windings inside, wires star, star.
An unusual setup for such a small motor.
Y is the symbol for star and the triangle is the symbol for delta.

It is probably cheaper to replace the motor with a single phase motor.
Unless you need variable speed.
In that case I would go for a 3ph 230v motor and a vfd

I can’t see any numbers after the triangle n the voltage area of the plate.
[automerge]1576428183[/automerge]
Something like this might do you well
You will have to check dimensions and shaft size etc

 
Take the original to a local industrial motor supplier and ask for a replacement to your spec. They will be able to sell you something suitable.
£100 to £150 would be my guess
 
Thanks a million for helping
Next step decide if I need variable speed control :)

Torque, can we tell what it currently is off the plate?


Will do that re supplier thanks!



Take the original to a local industrial motor supplier and ask for a replacement to your spec. They will be able to sell you something suitable.
£100 to £150 would be my guess
 
I think that motor will connect as 230V delta and run fine from a variable frequency drive - 380V Y is about 225V delta. The 240V single phase input VFDs drives only output 240V 3P, they don't step up to 415V.
I assume there's a terminal box with a cover you can remove ? Please post a photo of the inside of that showing clearly what's currently connected - and if there's a diagram inside the lid, post a photo of that as well.
 
I think it's a dual-speed pole-changing motor!

  • The speeds are probably 1370 / 680 rpm (not 80, which looks like it means the gearbox output but I don't think that's correct). Please could you look closely at the plate and see if it is in fact 680.
  • The configuration is shown as YYΔ I.e. there are two sets of 3-phase windings for the two speeds.
  • It gives two equal values for line current (both 0.75A) and two values for cos φ, one of which is much lower than the other (that's usually the low speed).

If it were a single-speed motor designed to run in either 230V delta / 380V star, it would show both voltages and two different line currents. If I am correct, then it requires 380V for normal running in delta and cannot be operated directly from a 230V single-to-three-phase inverter.

Let's see inside the terminal box!
 
Thanks all, this is great to have your input.

Opened the casted cover and found:
I can retake photo again if wires are too hard to see, seems like 3 are joined across with solder. A german friend translated for me.???
3-phase-wiring-question.png


see.
3.jpg
1.jpg
1.jpg



I think that motor will connect as 230V delta and run fine from a variable frequency drive - 380V Y is about 225V delta. The 240V single phase input VFDs drives only output 240V 3P, they don't step up to 415V.
I assume there's a terminal box with a cover you can remove ? Please post a photo of the inside of that showing clearly what's currently connected - and if there's a diagram inside the lid, post a photo of that as well.
[automerge]1576447925[/automerge]
I think it's a dual-speed pole-changing motor!

  • The speeds are probably 1370 / 680 rpm (not 80, which looks like it means the gearbox output but I don't think that's correct). Please could you look closely at the plate and see if it is in fact 680.
  • The configuration is shown as YYΔ I.e. there are two sets of 3-phase windings for the two speeds.
  • It gives two equal values for line current (both 0.75A) and two values for cos φ, one of which is much lower than the other (that's usually the low speed).

If it were a single-speed motor designed to run in either 230V delta / 380V star, it would show both voltages and two different line currents. If I am correct, then it requires 380V for normal running in delta and cannot be operated directly from a 230V single-to-three-phase inverter.

Let's see inside the terminal box!


Thank you
i just checked,you're right it is 680 (very hard to see), there are nine wheels with sprockets and chain, is that the speed control? the speed needed, im guessing 50 - 100 rpm
 

Attachments

  • 2.jpg
    114.7 KB · Views: 27
Last edited:
The terminal diagram cast into the cover is a generic one, showing the normal options of star for high voltage and delta for low. However, it may not actually apply to your motor, as such a configuration would invariably also be indicated by the two voltages being stamped on the plate, whereas you only have 380V.

Do you have a multimeter? If so, please could you confirm which terminals show continuity to which others.

If you look at the black terminal block moulding there are terminal labels moulded in next to the studs. Probably something like:
U1-V1-W1
V2-W2-U2
Or its mirror image.

If you have continuity U1-U2 and V1-V2 and W1-W2 but not U1-V1 then the dual speed thing may be a red herring.

If you have continuity U1-V1-W1 and U2-V2-W2 but not U1-U2 then it is indeed a dual winding, dual speed motor. The speeds would be selected with a 3-pole changeover switch on the panel.
 
The terminal diagram cast into the cover is a generic one, showing the normal options of star for high voltage and delta for low. However, it may not actually apply to your motor, as such a configuration would invariably also be indicated by the two voltages being stamped on the plate, whereas you only have 380V.

Do you have a multimeter? If so, please could you confirm which terminals show continuity to which others.

If you look at the black terminal block moulding there are terminal labels moulded in next to the studs. Probably something like:
U1-V1-W1
V2-W2-U2
Or its mirror image.

If you have continuity U1-U2 and V1-V2 and W1-W2 but not U1-V1 then the dual speed thing may be a red herring.

If you have continuity U1-V1-W1 and U2-V2-W2 but not U1-U2 then it is indeed a dual winding, dual speed motor. The speeds would be selected with a 3-pole changeover switch on the panel.


Thank you very much for taking the time to explain this, I don't have a multimeter but either way I have to organise a single phase 240v motor(preferably with speed control.
I don't have access to 3 phase.

How do I work out what is a good replacement, is another generic .25 kw motor ( with correct form factor (and shaft location) with speed of
1370 / 680 rpm the way to go?
 
Thank you very much for taking the time to explain this, I don't have a multimeter but either way I have to organise a single phase 240v motor(preferably with speed control.
I don't have access to 3 phase.

How do I work out what is a good replacement, is another generic .25 kw motor ( with correct form factor (and shaft location) with speed of
1370 / 680 rpm the way to go?

Is this on the right track?

 
On the subject of the original motor, I've missed a trick. I'm convinced now it's a Dahlander consequent pole 2-speed motor, which runs in double-star at full speed and in series delta at low speed with equal torque. You won't need the low speed mode as the VSD will do that for you, so you could run it on a 230V inverter by swapping the internal interconnections between the two winding groups so that the same relative coil polarities as are currently obtained in star are obtained in delta instead. That would give you a single-speed, 230V delta motor of full power rating. If you wanted to go down this route, I would need to see very detailed pics of the internal winding leadouts, and we would have to pick through them with a continuity tester very carefully to ensure we make the right interconnections.
 
On the subject of the original motor, I've missed a trick. I'm convinced now it's a Dahlander consequent pole 2-speed motor, which runs in double-star at full speed and in series delta at low speed with equal torque. You won't need the low speed mode as the VSD will do that for you, so you could run it on a 230V inverter by swapping the internal interconnections between the two winding groups so that the same relative coil polarities as are currently obtained in star are obtained in delta instead. That would give you a single-speed, 230V delta motor of full power rating. If you wanted to go down this route, I would need to see very detailed pics of the internal winding leadouts, and we would have to pick through them with a continuity tester very carefully to ensure we make the right interconnections.

:)You're Brilliant! if you're up for a challenge I can follow your instructions to a tee,its a beast of a power feed, aprox 120 kg. I will need to get a mulitmeter/continuity tester, I presume I need to unmount from the gearbox and open it up and take pics of the windings?
Im a trained engineering technician but complicated electrics not my forte:)
 

Attachments

  • this_is_the_final_destination_).png
    238.8 KB · Views: 26
Disclaimer:
Some time will need to be invested to find out whether it is possible at all.
There is a high risk of accidental error with the windings as there are millions of permutations of 12 wires (six windings each with two ends). If they get mixed up or we mis-identify them, it will be slow and tricky to identify the proper phasing again without specialist equipment. Getting one winding out of phase for example, could result in poor torque, blown fuses, burnout, inverter destruction or all of the above. So proceed at your own risk.

As there only seems to be one lead from inside the motor to each terminal stud (please confirm), the connections must be within the end bell so you would have to get inside there to swap them over. If they are hidden or bound up with winding tape it could be tricky. I suppose you've nothing to lose by looking inside though.

@marconi @Marvo @darkwood and anyone else please check my logic:

a) It has to be a Dahlander connection as-is.
b) There are 6 leads in the terminal box for 12 winding ends so they must be paired internally into series delta.
c) The edges of the delta (2U, 2V, 2W) can remain connected as-is, as this gives the right relative polarity of both windings of each phase for high-speed.
d) The corners of the delta (1U, 1V, 1W) need to be split so that the two windings of each phase can be paralleled.
e) The paralleled windings can then be connected in delta to make a 3-lead 230V motor.

One snag we have now is that we don't know for certain which set of leads are the edges and which are the corners. We might assume that terminal block 1U= winding U1 = corner terminal etc but there's no guarantee because the original speed switching has been disconnected. If we can see the windings leading out from their respective coils, that's fine. Otherwise we might have to use a battery and compass in the bore, or feed in low voltage AC e.g. from a bell transformer and find coil phasing by searching with a voltmeter.

I'll post a diagram later.
 
Last edited:
Disclaimer:
Some time will need to be invested to find out whether it is possible at all.
There is a high risk of accidental error with the windings as there are millions of permutations of 12 wires (six windings each with two ends). If they get mixed up or we mis-identify them, it will be slow and tricky to identify the proper phasing again without specialist equipment. Getting one winding out of phase for example, could result in poor torque, blown fuses, burnout, inverter destruction or all of the above. So proceed at your own risk.

As there only seems to be one lead from inside the motor to each terminal stud (please confirm), the connections must be within the end bell so you would have to get inside there to swap them over. If they are hidden or bound up with winding tape it could be tricky. I suppose you've nothing to lose by looking inside though.

@marconi @Marvo @darkwood and anyone else please check my logic:

a) It has to be a Dahlander connection as-is.
b) There are 6 leads in the terminal box for 12 winding ends so they must be paired internally into series delta.
c) The edges of the delta (2U, 2V, 2W) can remain connected as-is, as this gives the right relative polarity of both windings of each phase for high-speed.
d) The corners of the delta (1U, 1V, 1W) need to be split so that the two windings of each phase can be paralleled.
e) The paralleled windings can then be connected in delta to make a 3-lead 230V motor.

One snag we have now is that we don't know for certain which set of leads are the edges and which are the corners. We might assume that terminal block 1U= winding U1 = corner terminal etc but there's no guarantee because the original speed switching has been disconnected. If we can see the windings leading out from their respective coils, that's fine. Otherwise we might have to use a battery and compass in the bore, or feed in low voltage AC e.g. from a bell transformer and find coil phasing by searching with a voltmeter.

I'll post a diagram later.
Mega cool of you and the forum! I fully accept this might not be possible or work at all. I will get to work removing it from gearbox and sharing all the info depth info u need. I wanted to know more about motors, this is a premium learning exercise!
X mas is coming up fast, understand if this waits until NY. Again amazingly cool of you and the forum. :)
 
wow, you are getting not beyond my understanding but certainly out of my comfort zone.

not sure if I understand correctly what you are referring to when describing the windings but have got as far as this poorly drawn representation. left (as is) right (convert to)

am I with you so far?

its been a long time since I was sat in a hall figuring out if it was the left hand or right hand that I should be putting into silly positions for the solution.
 

Attachments

  • IMG_1223.jpg
    62.6 KB · Views: 26

Reply to what do these 380v wiring colours mean, I want to use with a 220v vfd. it may have had speed control in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Posted this to the DIY section since I'm not a business or employee in this matter but it feels more appropriate (and might actually get...
Replies
0
Views
788
Hello, DIYer and first time poster here. Recently bought a house built in 1925, and am gradually working through adding and replacing the wiring...
Replies
9
Views
2K
Hi All, A mate of mine recently acquired a rather nice wood turning lathe they'd like to get running out in their workshop. However he admits his...
Replies
1
Views
1K
Hi everyone, I want to install a wifi switch in my room but the problem is I am not very informed in electrical wiring subject so would appreciate...
Replies
3
Views
1K
M
It's not car related but is a 12vdc porject, so hope someone can be of help to me on this project I’m a bit of an amateur photographer when it...
Replies
2
Views
2K
mollydog
M

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock