Discuss What is PME and TNCS?? in the Australia area at ElectriciansForums.net

G

Guest112

Hi guys just wondering if someone can explain the difference between the two, was doing a pir today and whilst checking the supply i noticed a western power sticker on their cut out saying the earthing arrangement is either PME or TNCS. But on the reports my company uses the only options to tick regarding the supply are
1. TNCS Pme
2. TNCS protective neutral bond

I know about supplys and im aware that tncs is tera neutral combined seperate being that the neutral and earth is combined to the cutout and separate to the installation via a separate earth off the neutral and so on so can someone explain the PME for me please and how/if its different in the installation?? And a PEN also??? Cheers guys
 
Hi Peter, firstly, PME and PNB are both classed as TN-C-S supplies which as you rightly state, consist of a PEN conductor which is separated at the point of use into neutral and earth conductors.

The difference is in the M of PME, meaning 'multiple'. The PEN conductor on PME is tied down to earth at Multiple points along it's route.

On PNB, there is a PEN conductor but this is only connected to earth at 1 point and is normally limited to situations where a distribution transformer supplies only 1 consumer.
 
Hi IQ, is there any way of determining that a transformer is only serving 1 customer? I guess if it's a pole transformer and the overheads don't go on any further and this "last pole" is at a farm in the middle of nowhere that's a good clue, but is there a more scientific way? Thanks, SW
 
PME is protective mutiple earthing, where the protective conductor, PEN conductor) will be earted along its route, usually with rods attached at underground joints, or from overhead lines. As far as im aware, a protecive neutral bond, is where the neutral bar and earth bar within larger electrical distribution opanels are linked together, rather than linking the star point to earth at the supply transformer.
 
Hi IQ, is there any way of determining that a transformer is only serving 1 customer? I guess if it's a pole transformer and the overheads don't go on any further and this "last pole" is at a farm in the middle of nowhere that's a good clue, but is there a more scientific way? Thanks, SW

Hi SW, unless you've got information from the supplier (rare) then you can only go on what you can see.
 
Hi Peter, firstly, PME and PNB are both classed as TN-C-S supplies which as you rightly state, consist of a PEN conductor which is separated at the point of use into neutral and earth conductors.

The difference is in the M of PME, meaning 'multiple'. The PEN conductor on PME is tied down to earth at Multiple points along it's route.

On PNB, there is a PEN conductor but this is only connected to earth at 1 point and is normally limited to situations where a distribution transformer supplies only 1 consumer.


TNC-S can also be a DNO supply cable that is in the process of PME, but hasn't yet reached the max Ze level of 0.35 ohms or doesn't yet comply with PME designated requirements. If the truth be known, there are many such situations around the country from what i can make of it. A true PME supply should have the neutral roded at every joint in the supply cable string. This has nothing to do with the supplying transformer, it's the cable that is providing the earth system....
 
Hi Peter, firstly, PME and PNB are both classed as TN-C-S supplies which as you rightly state, consist of a PEN conductor which is separated at the point of use into neutral and earth conductors.

The difference is in the M of PME, meaning 'multiple'. The PEN conductor on PME is tied down to earth at Multiple points along it's route.

On PNB, there is a PEN conductor but this is only connected to earth at 1 point and is normally limited to situations where a distribution transformer supplies only 1 consumer.

so is a tncs always earthed at points along the route (PME) and if so is PME just another term for the arrangement?
And the PEN conductor on a tncs is the name of the neutral earth conductor what does it stand for lol
And a PNB protective neutral bond is an individual supply from a transformer is that correct? much apreciated btw
 
so is a tncs always earthed at points along the route (PME) and if so is PME just another term for the arrangement?
And the PEN conductor on a tncs is the name of the neutral earth conductor what does it stand for lol
And a PNB protective neutral bond is an individual supply from a transformer is that correct? much apreciated btw

Think of PME as a high integrity TNC-S system. PEN stands for ...Protective Earthed Neutral.
 
Last edited by a moderator:
I bet that bloke at the "joint box house" we were at the other week STILL hasn`t been on to the DNO about getting that old cast iron cutout replaced and a TN-C-S earthing arrangement n all.....still on a TT that one...................
 
so is a tncs always earthed at points along the route (PME) and if so is PME just another term for the arrangement?
And the PEN conductor on a tncs is the name of the neutral earth conductor what does it stand for lol
And a PNB protective neutral bond is an individual supply from a transformer is that correct? much apreciated btw

A PNB isnt always a supply from a dedicated transformer. A protective neutral bond is the link between the star point of the transformer, and the earth grid of the transformer. This joint could be made at the transformer itsself, or could be made at the consumers main distribution panel. The latter option is only taken (in my experience) in larger installations.
 
If the transformer supplies more than one consumer the DNO will fit a service pillar near the transformer and install the N-E link there. They will not fit the link at a consumer’s switchboard unless it’s a sole supply.
 
Last edited by a moderator:

Reply to What is PME and TNCS?? in the Australia area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
571
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
727
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
3K
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock