@ToonSparky is correct to terminate into the board before testing, at least for the CPCs anyway. If you're not connecting the CPCs to the earthing arrangement, then your IR testing is non compliant:

643.3.1 The insulation resistance shall be measured between live conductors and between live conductors and the protective conductor connected to the earthing arrangement

GN3 (17th ed, am3) tells me that this requirement came in in 2008, prior to this you could just test to the CPC without it terminated. Old habits die hard huh?
Maybe this is why I was taught to do it this way back when I was an apprentice.

So it could be worthwhile carrying out all R1+R2 and end to end tests while disconnected from the board but IR tests onwards cables should be terminated?
 
Maybe this is why I was taught to do it this way back when I was an apprentice.

So it could be worthwhile carrying out all R1+R2 and end to end tests while disconnected from the board but IR tests onwards cables should be terminated?
Sure, no reason I can think of why you shouldn't do it that way. Much easier to find which conductor belongs to which leg of a ring final for the fig.of 8 tests if you do it before the cables are terminated
 
Am I being completely thick , but why? do you need to connect the earths to the earth bar to conduct your initial IR tests

at college we did dead tests prior to connecting circuits to the board
 
@Dustydazzler
This is done so that any cable that may have become damaged during installation is tested to earth as well. That way you can be sure there is definitely no faults through say the building steel ect that would have been missed by doing the test disconnected from the earth bar. If that makes sense
 
Last edited:
Am I being completely thick , but why? do you need to connect the earths to the earth bar to conduct your initial IR tests

at college we did dead tests prior to connecting circuits to the board
@Dustydazzler
This is done so that any cable that may have become damaged during installation is tested to earth as well. That way you can be sure there is definitely no faults through say the building steel ect that would have been missed by doing the test disconnected from the earth bar. If that makes sense
Although there is nothing to stop you IR testing circuit lives to incoming CPC, or MET if local, as well as circuit CPC to tick that box.

IR becomes a five point test (obviously not TPN) instead of three but the ease of access and not having to redress the CU makes it worth it.
 

Reply to What makes you question things? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock