Currently reading:
What makes you question things?

Discuss What makes you question things? in the UK Electrical Forum area at ElectriciansForums.net

IAmSparkytus!

-
Esteemed
Arms
Reaction score
315
Evening all,

Was thinking the other day about an installation I've seen where the 2 earths of a ring main at the DB were covered in one sheath of sleeving.

This made me wonder whether end to end tests would have been carried out or not. Would someone do the tests and then put the sleeving on?

I know I make off a board and then carry out the testing when all cables are terminated.

Are there any other things you all come across which make you question whether things might have been missed?
 
I get the sleeving on asap myself, as I dislike bare copper flying around, especially if the incomer is live on the supply side or if it's a 3 phase board.
No reason why someone couldn't test and then sleeve though.
It's also theoretically possible the end to ends might have been done at a socket.
 
Last edited:
Evening all,

Was thinking the other day about an installation I've seen where the 2 earths of a ring main at the DB were covered in one sheath of sleeving.

This made me wonder whether end to end tests would have been carried out or not. Would someone do the tests and then put the sleeving on?

I know I make off a board and then carry out the testing when all cables are terminated.

Are there any other things you all come across which make you question whether things might have been missed?
Sorry to be pedantic but it's a ring final circuit not a ring main.
But I do get what you're getting at. Attention to details is important in this job, and a lack thereof can lead one to question the integrity of the workmanship as a whole...
 
In theory you could twist all the cpcs from every single circuit together as one big twisted mess and put under just one single length of wide earth sleeve.…

the next bloke would have a wonderful time trying to work out what the heck is going on
 
Old habit of wanting to second fix everything including the DB before I test. Testings always last on my to do list.

Do most people test one circuit then terminate, then another and another until all are done?
Usually have all cables taped, marked and tested before the board goes on the wall.

Otherwise your wiring the board twice.

Much easier to to test as well.
 
I dead test before the cable gets anywhere near the new board. Once it’s dressed in the board it’s connected and that’s it. I can not get my head round doing the board then trying to test, that’s all backwards….
and....dead testing before connecting ensures you ain't got 1 leg of a RFC connected in with a radial instead of it's "correct" other leg.
 
@ToonSparky is correct to terminate into the board before testing, at least for the CPCs anyway. If you're not connecting the CPCs to the earthing arrangement, then your IR testing is non compliant:

643.3.1 The insulation resistance shall be measured between live conductors and between live conductors and the protective conductor connected to the earthing arrangement

GN3 (17th ed, am3) tells me that this requirement came in in 2008, prior to this you could just test to the CPC without it terminated. Old habits die hard huh?
 
@ToonSparky is correct to terminate into the board before testing, at least for the CPCs anyway. If you're not connecting the CPCs to the earthing arrangement, then your IR testing is non compliant:

643.3.1 The insulation resistance shall be measured between live conductors and between live conductors and the protective conductor connected to the earthing arrangement

GN3 (17th ed, am3) tells me that this requirement came in in 2008, prior to this you could just test to the CPC without it terminated. Old habits die hard huh?
Maybe this is why I was taught to do it this way back when I was an apprentice.

So it could be worthwhile carrying out all R1+R2 and end to end tests while disconnected from the board but IR tests onwards cables should be terminated?
 
Maybe this is why I was taught to do it this way back when I was an apprentice.

So it could be worthwhile carrying out all R1+R2 and end to end tests while disconnected from the board but IR tests onwards cables should be terminated?
Sure, no reason I can think of why you shouldn't do it that way. Much easier to find which conductor belongs to which leg of a ring final for the fig.of 8 tests if you do it before the cables are terminated
 
Am I being completely thick , but why? do you need to connect the earths to the earth bar to conduct your initial IR tests

at college we did dead tests prior to connecting circuits to the board
 

Reply to What makes you question things? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock